06/2018
›
Logic Controller
Millenium Evo
›
Up to 44 I/Os - 16 DI (4 HighSpeed /
8 AI) - 8 DO
with bluetooth Interface and Crouzet
Virtual Display
›
Wireless programming & Control
›
Modbus RTU Network (Slave)
›
Local datalog management
›
Up to 1000 programing blocks with
intuitive Crouzet Soft to go from
simple to complex applications
XBP24
Base 24 I/O
XBP24-E
Base 24 I/O Ethernet
XDP24
Base 24 I/O
XDP24-E
Base 24 I/O Ethernet
Product selection
LCD display
No
No
Yes
Yes
Product selection KIT
Bluetooth Kit (Millenium EVO Ethernet 88 975 111, Bluetooth interface 88 980 112,
Bluetooth receiver 88 980 116)
Bluetooth Kit (Millenium EVO Standalone 88 975 101, Bluetooth interface 88 980 112,
Bluetooth receiver 88 980 116)
XBP24
General characteristics
Part number
Products certification
Conformity with the low voltage directive
(in accordance with 2014/35/EU)
Conformity with the EMC directive
(in accordance with 2014/30/EU)
88 975 001
CE, cULus Listed
IEC/EN 61131-2 (Open equipment)
IEC/EN 61000-6-1 (Residential, commercial and light-industrial environments)
IEC/EN 61000-6-2 (Industrial)
IEC/EN 61000-6-3 (Residential, commercial and light-industrial environments)
IEC/EN 61000-6-4 (Industrial)
Power supply earthing
Overvoltage category
Pollution
Maximum utilization altitude
Mechanical resistance
Resistance to electrostatic discharge
Resistance to HF interference
(Immunity)
None
3 in accordance with IEC/EN 60664-1
Degree : 2 in accordance with IEC/EN 61131-2
Operation: 2000 m
Transport: 3000 m
Immunity to vibrations IEC/EN 60068-2-6, Fc test
Immunity to shock IEC/EN 60068-2-27, Ea test
Immunity to ESD IEC/EN 61000-4-2, level 3
Immunity to radiated electrostatic fields IEC/EN 61000-4-3, level 3
Immunity to fast transients (burst immunity) IEC/EN 61000-4-4, level 3
Immunity to shock waves IEC/EN 61000-4-5
Radio frequency in common mode IEC/EN 61000-4-6, level 3
Conducted and radiated emissions
(in accordance with EN 55022/11 group 1)
Operation temperature
Class B
-20 °C (-4 °F) → +60 °C (140 °F) (+40 °C (104 °F) in a non-ventilated enclosure)
UL: maximum surrounding air: +50 °C (122 °F)
88 975 011
88 975 101
88 975 111
XBP24-E
XDP24
Ethernet network
No
Yes
No
Yes
Part number
88 975 001
88 975 011
88 975 101
88 975 111
88 975 911
88 975 901
XDP24-E
Standard product
Product made to order
Contact us
|
AUTOMATION.CROUZET.COM
|2
|
Logic Controller
|
06/2018
XBP24
Storage temperature
Relative humidity
Screw terminals connection capacity
XBP24-E
XDP24
XDP24-E
-40°C (-40 °F) → +80°C (176 °F)
95% max. (no condensation or dripping water)
Flexible wire with ferrule: 1 conductor: 0.2 to 2.5 mm2 (AWG 24-14)
Flexible wire with ferrule: 2 conductors: 0.2 to 0.75 mm2 (AWG 24-18)
Rigid wire: 1 conductor: 0.2 to 2.5 mm2 (AWG 24-14)
Rigid wire: 2 conductors: 0.2 to 0.75 mm2 (AWG 24-18)
Tightening torque: 0.5 N.m (4.5 lb-in) (tighten using screwdriver diam. 3.5 mm)
Stripping length: 6 mm
Material
Environnement
On front panel color
On sole color
Protection rating
(in accordance with IEC/EN 60529)
Weight
Dimensions
Lexan, UL94V0
Reach, RoHS, Halogen free 1272/2008/CE
Grey RAL 7035
Black RAL 9011
IP 40 on front panel
IP 20 on terminal block
Without packing: 270 g
With packing: 320 g
Without packing: 300 g
With packing: 350 g
Without packing: 330 g
With packing: 380 g
Without packing:
124.6 x 90 x 62 mm / 4.91 x 3.54 x 2.44 inch
With packing:
148 x 103 x 65 mm / 5.83 x 4.06 x 2.56 inch
Display with 4 lines of 18 characters, yellow/
green
Without packing:
124.6 x 90 x 61.1 mm / 4.91 x 3.54 x 2.4 inch
With packing:
148 x 103 x 65 mm / 5.83 x 4.06 x 2.56 inch
Processing characteristics
LCD display
Programming method
Program size
Program memory
Removable memory
Data memory
Back-up time
(in the event of power failure)
Data back-up
Cycle time
Clock data retention
Clock drift
Without
FBD (Function Block Diagram), including SFC (Sequential Function Chart) (Grafcet)
Function blocks: typically 512 blocks
Macro blocks: 127 max. (255 blocks per macro)
Flash
N.A
2 k octets
Program and settings in the controller: 10 years
Data memory: 10 years
Data backup in the flash memory is guaranteed if the product is powered on more than 10 seconds
From 2 ms* to 90 ms, default value: 10 ms
*: Depending on configuration
10 years (lithium battery) at 25°C (77°F)
Drift < 12 min/year (at 25°C (77°F))
6 s / month (at 25°C (77°F) with user-definable correction of drift).
Synchronizable by network
Timer block accuracy
Start up time on power up
0.5 % ± 2 cycle time
< 8 s base alone, < 5 s
base + 2 expansions +
1 accessory (RS485)
< 10 s base alone, < 5
s base + 2 expansions
+ 1 accessory (RS485)
< 8 s base alone, < 5 s
base + 2 expansions +
1 accessory (RS485)
< 10 s base alone, < 5
s base + 2 expansions
+ 1 accessory (RS485)
Self test
Test firmware integrity (checksum memory)
Stability of the internal power supply
Check the conformity of the em4 device configuration with the configuration in the application
program.
Supply
Nominal voltage
Operating limits
Immunity from micro power cuts
Max. absorbed power
24 VDC (-15% / +20%)
20.4 - 28.8 VDC
≤ 1 ms (repetition 20 times)
3.8 W @ 24 VDC, 5 W
@ 28.8 VDC,
1.5 W @ 24 VDC I/O
OFF
4.8W @ 24 VDC, 6.2
W @ 28.8 VDC,
1.5W @ 24 VDC I/O
OFF
4W @ 24 VDC, 5.3 W
@ 28.8 VDC, - 0.3 W
backlight OFF
1.5W @ 24 VDC (I/O
+ backlight) OFF
5W @ 24 VDC, 6.5 W
@ 28.8 VDC, - 0.3 W
backlight OFF
1.5W @ 24 VDC (I/O
+ backlight) OFF
|
AUTOMATION.CROUZET.COM
|3
|
Logic Controller
|
06/2018
XBP24
Protection against polarity inversions
Power monitoring
Inputs
Digital and high speed digital inputs 24 VDC - 4 inputs from I1 to I4
Input used as digital input
Input voltage
Input current
24 VDC (-15% / +20%)
1.8 mA @ 20.4 V
2.1 mA @ 24 V
2.5 mA @ 28.8 V
Input impedance
Logic 1 voltage threshold
Making current at logic state 1
Logic 0 voltage threshold
Release current at logic state 0
Response time
Sensor type
Conforming to IEC/EN 61131-2
Input type
Isolation between power supply and inputs
Isolation between inputs
Protection against polarity inversions
Status indicator
Cable length
Input used as high speed digital input
Maximum counting frequency
11.6 kΩ
≥ 15 VDC
≥ 1.3 mA
≤ 10 VDC
≤ 0.8 mA
1 to 2 cycle times
Contact or 3-wire PNP
Type 1
Resistive
None
None
Yes
No
≤ 100 m
Yes
XBP24-E
XDP24
XDP24-E
Yes and value available through the application «FB Status», 1/10V, 5%.
On LCD screen
3 channels encoder (I1, I2, I3): 5 kHz*
2 independent counters (I1, I2) (I3, I4) (Cumul, IND, DIR): 2 channels: 10 kHz*,
4 channels: 5 kHz*,
2 independent counters (I1, I2) (I3, I4) (PH, PH2): 2/4 channels: 5 kHz*
4 independent counters (I1, I2, I3, I4) (Up/Down) : 1 channel: 15 kHz*, 2 channels: 10 kHz*, > 2
channels: 5 kHz*
* with a time cycle ≤ 10 ms and a ton / toff = 50% ± 5%, level 0 < 2V and level 1 > 20,4V
Other functions
Cable length
Input used as digital input
Input voltage
Input current
4 tachometers (I1, I2, I3, I4 )
≤ 3 m with shielded twisted cable
Digital 24 VDC and analog inputs 12 bits / 28.8 V - potentiometer - 8 inputs from I5 to IC
24 VDC (-15% / +20%)
1.8 mA @ 20.4 V
2.1 mA @ 24 V
2.5 mA @ 28.8 V
Input impedance
Logic 1 voltage threshold
Making current at logic state 1
Logic 0 voltage threshold
Release current at logic state 0
Response time
Sensor type
Conforming to IEC/EN 61131-2
Input type
Isolation between power supply and inputs
Isolation between inputs
Protection against polarity inversions
11.6 kΩ
≥ 11 VDC
≥ 1 mA
≤ 9 VDC
≤ 0.7 mA
1 to 2 cycle times
Contact or 3-wire PNP
Type 1
Resistive
None
None
Yes
|
AUTOMATION.CROUZET.COM
|4
|
Logic Controller
|
06/2018
XBP24
Status indicator
Cable length
Input used as analog input
Measuring range
Input impedance
Maximum value without destruction
Input type
Resolution
Value of LSB
Conversion time
Maximum error in 0-10V mode
Maximum error in 0-V power supply mode
Repeat accuracy at 55°C (131°F)
Voltmeter
Isolation between analogue channel and
power supply
Protection against polarity inversions
Potentiometer control
Cable length
Digital 24 VDC - 4 inputs from ID to IG
Input voltage
Input current
24 VDC (-15% / +20%)
1.5 mA @ 20.4 V
1.7 mA @ 24 V
2.1 mA @ 28.8 V
Input impedance
Logic 1 voltage threshold
Making current at logic state 1
Logic 0 voltage threshold
Release current at logic state 0
Response time
Sensor type
Conforming to IEC/EN 61131-2
Input type
Isolation between power supply and inputs
Isolation between inputs
Protection against polarity inversions
Status indicator
Cable length
Outputs
6 A relay output - 2 outputs from O1 to O2
Breaking voltage
Breaking current
Maximum breaking current in the common
Mechanical life
250 VAC max
6A
13.9 kΩ
≥ 11 VDC
≥ 0.8 mA
≤ 8 VDC
≤ 0.5 mA
1 to 2 cycle times
Contact or 3-wire PNP
Type 1
Resistive
None
None
No
No
≤ 30 m
No
≤ 30 m
XBP24-E
XDP24
On LCD screen
XDP24-E
0 → 10 V, 0 → V power supply or Voltmeter
11.6 kΩ
28.8 VDC max
Common mode
12 bit at maximum input voltage (10 bit at 10V)
7.03 mV
Controller cycle time
± 3.5 % of full scale at 25°C (77°F)
± 5 % of full scale at 55°C (131°F)
± 5 % of full scale at 25°C (77°F)
± 6.2 % of full scale at 55°C (131°F)
±2%
From 0 to 30.5 V, 5%
None
Yes
2.2 kΩ / 0.5 W (recommended), 10 KΩ max.
≤ 10 m with shielded twisted cable (sensor not isolated)
On LCD screen
Derating: UL: ≥ 45°C (113°F): 4A max
IEC @ 25°C (77 °F): 12 A
IEC @ 60°C (140 °F) or UL: 10 A
5 000 000 operations (cycles)
|
AUTOMATION.CROUZET.COM
|5
|
Logic Controller
|
06/2018
XBP24
Electrical durability for 50 000 operating
cycles
XBP24-E
XDP24
XDP24-E
24 VDC tau = 0 ms: 6 A, tau = 7 ms: 3 A, tau = 15 ms: 1.8 A
Usage category DC-12: 24 V, 6 A
Usage category DC-14: 24 V, 1.8 A
250 VAC cos phi = 1: 6 A, cos phi = 0.7: 5 A, cos phi = 0.4: 2.5 A
Usage category AC-12: 250 V, 6 A
Usage category AC-13: 250 V, 5 A
Usage category AC-15: 250 V, 2 A
Minimum switching capacity
Maximum operating rate
Voltage for withstanding shocks
Response time
Built-in protections
Status indicator
Cable length
8 A relay output - 6 outputs from O3 to O8
Breaking voltage
Breaking current
Maximum breaking current in the common
Mechanical life
Electrical durability for 50 000 operating
cycles
100 mA (at minimum voltage of 12V)
Off load: 10 Hz
At operating current: 0.1 Hz
In accordance with IEC/EN 60947-1 and IEC/EN 60664-1: 4 kV
Make = 1 cycle time + 8 ms typical
Release = 1 cycle time + 4 ms typical
Against short-circuits: None
Against over voltages and overload: None
No
≤ 30 m
250 VAC max
8A
Derating: CEI ≥ 55°C (131°F) or UL: ≥ 45°C (113°F): 6A max
IEC @ 25°C (77°F): C3, C6: 8A ; C4, C5: 16 A
IEC @ 60°C (140 °F) or UL: C3, C6: 8 A ; C4, C5: 10 A
20 000 000 operations (cycles)
24 VDC tau = 0 ms: 8 A, tau = 7 ms: 3 A, tau = 15 ms: 1.5 A
Usage category DC-12: 24 V, 8 A
Usage category DC-14: 24 V, 1.5 A
250 VAC cos phi = 1: 8 A, cos phi = 0.7: 4.75 A, cos phi = 0.4: 3 A
Usage category AC-12: 250 V, 8 A
Usage category AC-13: 250 V, 4.3 A
Usage category AC-15: 250 V, 1.5 A
On LCD screen
Minimum switching capacity
Maximum operating rate
Voltage for withstanding shocks
Response time
Built-in protections
Status indicator
Cable length
Ethernet network
Programming / exploitation
Ethernet connection
Adressage
100 mA (at minimum voltage of 12V)
Off load: 10 Hz
At operating current: 0.1 Hz
In accordance with IEC/EN 60947-1 and IEC/EN 60664-1: 4 kV
Make = 1 cycle time + 10 ms typical
Release = 1 cycle time + 5 ms typical
Against short-circuits: None
Against over voltages and overload: None
No
≤ 30 m
-
-
-
USB & Ethernet port /
Ethernet port
Type RJ45, 10/100
Mbit/s, MDI/MDIX
Static or dynamic
(DHCP server / Auto
IP)
Modbus TCP (client
/ server), Discovery,
UDP, TCP, SMTP, SSL
(workshop communi-
cation via Ethernet)
Maximun length
between 2 devices:
100 m / 3937 inch
-
-
-
USB & Ethernet port /
Ethernet port
Type RJ45, 10/100
Mbit/s, MDI/MDIX
Static or dynamic
(DHCP server / Auto
IP)
Modbus TCP (client
/ server), Discovery,
UDP, TCP, SMTP, SSL
(workshop communi-
cation via Ethernet)
Maximun length
between 2 devices:
100 m / 3937 inch
On LCD screen
Protocols
-
-
Cable length
-
-