Switching Power Supply
Industrial Power Supply with Power
Factor Correction
Meets EN61000-3-2 (limits for harmonic current
emissions) with PFC on 100 to 600 W.
Suitable for universal usage, conforming to
EN50081-1 (Non-PFC models).
Models range from 100 to 600 W.
A wide input voltage range: 100 to 240 VAC
UL, CSA, VDE, and IEC (EN) safety conformance
EMC conformance
Three-year guarantee
Long life expectancy: 10 years min.
S82H
RC
Output voltage
5V
12 V
15 V
24 V
9A
7.2 A
4.6 A
30 A
13.5 A
10 A
7A
20 A
9A
7.2 A
4.6 A
30 A
13.5 A
10 A
7A
60 A
27 A
20 A
14 A
120 A
53 A
40 A
27 A
Output current
20 A
Models
S82H-10005
S82H-10012
S82H-10015
S82H-10024
S82H-15005
S82H-15012
S82H-15015
S82H-15024
S82H-P10005
S82H-P10012
S82H-P10015
S82H-P10024
S82H-P15005
S82H-P15012
S82H-P15015
S82H-P15024
S82H-P30005
S82H-P30012
S82H-P30015
S82H-P30024
S82H-P60005
S82H-P60012
S82H-P60015
S82H-P60024
Ordering Information
PFC
No
Output capacity
100 W
150 W
5V
12 V
15 V
24 V
Yes
100 W
5V
12 V
15 V
24 V
150 W
5V
12 V
15 V
24 V
300 W
5V
12 V
15 V
24 V
600 W
5V
12 V
15 V
24 V
Accessories (Order Separately)
Applicable power
supply
S82H-j100jj
S82H-j150jj
S82H-P300jj
S82H-P600jj
Bottom-mounting
S82Y-H10B
S82Y-F15B
S82Y-D30B
S82Y-D60B
Side-mounting
S82Y-H10S
S82Y-F15S
S82Y-D30S
S82Y-D60S
Front-mounting
Back-mounting
S82Y-H10F
---
---
---
---
---
S82Y-DFAN
S82Y-DFAN
Fan
Terminal
Expansion Bracket
---
---
---
S82Y-D60T
1
S82H
Model Number Legend
S82H -
1
2
3
Conversion Table
Conventional model
S82H-3005
1. Power Factor Correction
None:No
P:
Yes
2. Output Capacity
100: 100 W
150: 150 W
300: 300 W
600: 600 W
3. Output Voltage
05: 5 V
12: 12 V
15: 15 V
24: 24 V
S82H-3012
S82H-3024
S82F-1512
S82F-1524
New model
S82H-10005
S82H-10012
S82H-10024
S82H-15012
S82H-15024
S82H
Specifications
Ratings/Characteristics
Item
No
100 W
Efficiency
Life expectancy (see note 1.)
Input
Voltage
150 W
100 W
150 W
70% to 86% (depending on the model)
10 years min. in standard installation conditions at 40°C at the rated input with 50% load.
100 to 120 VAC/200 to
240 VAC (selectable) (85 to
132 VAC/170 to 264 VAC)
47 to 450 Hz
at 100-V input
at 200-V input
Leakage current
(See note 2.)
Inrush current
(See note 2.)
Power factor
Output
Voltage adjustment range
Ripple
Input variation influence
Load variation influence
Temperature variation influence
at 100-V input
at 200-V input
at 100-V input
at 200-V input
2.5 A max.
1.5 A max.
0.5 mA max.
1 mA max.
25 A max.
50 A max.
0.5 to 0.7
(depending on the model)
2% (p-p) max.
0.4 % max. (at 85- to 132-VAC/170- to 264-VAC input, 100% load)
0.8% max. (with rated input voltage, 0 to 100% load)
0.05%/°C max. (with rated I/O
at an ambient temperature
range between 0°C to 50°C)
0.8 s max. (Rises up to 90% of
the rated voltage under rated
input.)
20 ms min.
105% max. of rated load current, inverted L drop type, automatic
reset
105% max. of rated load
current, inverted L drop type,
automatic reset (output shut off
after 5 s, reset by input reset)
Yes, up to two Units
0.05%/°C max. (with rated I/O at an ambient temperature range
between 0°C to 40°C)
1 s max. (Rises up to 90% of the rated voltage under rated input.)
0.95
4 A max.
2.5 A max.
100 to 240 VAC (85 to 264 VAC)
PFC
Yes
300 W
600 W
Frequency
Current
47 to 63 Hz
1.7 A max.
0.85 A max.
2.5 A max.
1.3 A max.
5 A max.
2.5 A max.
0.75 mA max.
1.5 mA max.
10 A max.
5 A max.
1 mA max.
2.0 mA max.
±10%
(adjustable with variable resistor (V.ADJ))
Rise time
Hold time
Additional
function
Overload protection
Overvoltage protection
Parallel operation
Series operation
Remote sensing
Remote control
Remote voltage adjustment
Cooling method
Fan alarm function
120% of rated output voltage (typical), shutoff type, input reset
No
Yes
Yes
No
Yes
Natural air-cooling used
No
Forced air-cooling with built-in
fan
Yes
Yes
No
Yes
Yes, up to five
Units
No
Yes, up to five
Units
2
S82H
Item
No
100 W
Other
Ambient temperature
Ambient humidity (operating)
Dielectric strength
150 W
100 W
150 W
PFC
Yes
300 W
S82H
600 W
Operating: See the derating curve in the “Engineering Data” section. No condensation or icing.
Storage:
–25°C to 65°C with no condensation or icing
25% to 85%
3 kVAC, 50/60 Hz for 1 min between all inputs and all outputs with a current leakage of 25 mA max.
2.5 kVAC, 50/60 Hz for 1 min between all inputs and GR terminals with a current leakage of 25 mA
max.
1.0 kVAC, 50/50 Hz for 1 min between all outputs and GR terminals with a current leakage of 15 mA
max. for each 100-W model, 20 mA max. for each 150-W model, 25 mA max. for each 300-W
model, and 50 mA max. for each 600-W model. (See note 3.)
100 MΩ min. between all outputs and all inputs/GR terminals at 500 VDC (See note 3.)
Malfunction: 10 to 55 Hz, 0.375-mm single amplitude for 2 hrs each in X, Y, and Z directions
Malfunction: 300 m/s
2
(approx. 30G), 3 times each in
±X, ±Y,
and
±Z
directions
Yes (green)
Emission Enclosure:
Emission AC Mains:
Immunity ESD:
Immunity RF-interference:
Immunity Conducted Disturbance:
Immunity Burst:
EN55011 Group 1 class A (PFC models)
EN55022 Group 1 class B (Non-PFC models)
EN55011 Group 1 class A (PFC models)
EN55022 Group 1 class B (Non-PFC models)
EN61000-4-2: 4 kV contact discharge (level 2)
8 kV air discharge (level 3)
ENV50140:
10 V/m (10 k to 1 GHz) (level 3)
ENV50141:
10 V (0.15 to 80 MHz) (level 3)
EN61000-4-4: 2 kV power-line (level 3)
2 kV I/O signal-line (level 4)
Conforms to EN61000-3-2, IEC1000-3-2
Conforms to EN50081-2, EN50082-2
Conforms to FCC class A
1,050 g max.
1,850 g max.
3,500 g max.
5,500 g max.
Insulation resistance
Vibration resistance
Shock resistance
Output indicator
EMC
Limits for harmonic current
emission
EMC standards
Electromagnetic interference
Approved standards
Weight
---
Conforms to EN50081-1,
EN50082-2
Conforms to FCC class B
950 g max.
1,800 g max.
UL1012, CSA E.B. 1402C, VDE 0160, IEC 950, EN 60950
Note:
1. The fan is one of the replacement parts.
2. As defined with the rated input voltage and rated output voltage/current.
3. A surge absorber is provided for the input circuits of 300 and 600-W models. To test the dielectric strength and insulation resistance
of these models, remove the short bar attached across the GR and ACG terminals.
3
S82H
S82H
Engineering Data
Derating Curve
Units cannot be mounted vertically.
With No PFC
Standard Mounting
(100- and 150-W Models)
Forced
air-cooling
With PFC
Standard Mounting
(100-, 150-, 300-, and 600-W Models)
Forced air-cooling (100-
and 150-W Models only)
Load (%)
Natural air-
cooling
Load (%)
Natural air-
cooling
Ambient temperature (°C)
Ambient temperature (°C)
Horizontal Mounting (Applicable to 100- and 150-W Models)
Side Mounting (Applicable to 150-W Models Only)
Forced
air-cooling
Horizontal Mounting
(Applicable to 100- and 150-W Models Only)
Side Mounting (Applicable to 150-W Models Only)
Forced
air-cooling
Load (%)
Load (%)
Natural air-
cooling
Natural air-
cooling
Ambient temperature (°C)
Ambient temperature (°C)
Mounting Position
Standard Mounting
Horizontal Mounting
(Applicable to 100- and 150-W Models Only)
Side Mounting
(Applicable to 150-W Models Only)
Note:
Forced air-cooling must be applied at an minimum air capacity rate of 1 m
3
/min.
4
S82H
Overload Protection
The Power Supply is provided with an overload protection function
that protects the load and the power supply from possible damage
by overcurrent. When the output current rises above a set value
(105% of the rated output current for S82H), the protection function
is triggered, decreasing the output voltage. When the output current
falls within the rated range, the overload protection function is auto-
matically cleared.
100- and 150-W Models
S82H
In addition to the protection described in the left column, in the case
of the 300- and 600-W models, if the low voltage condition continues
for more than 5 s, shut off the output. In this situation, reset is not
automatic. The input power must be turned off for at least 1 minute,
and then turned on again to reset the Power Supply.
300- and 600-W Models
Rated
voltage
Output voltage (V)
Output voltage (V)
Rated
voltage
Output current (%)
Output current (%)
Note:
If the product is continuously used under short-circuit or overcurrent conditions, deterioration or damage to internal elements may
occur.
Overvoltage Protection
The Power Supply is provided with an overvoltage protection function that protects the load and the Power Supply from possible damage by
overvoltage. When the output voltage rises above a set value (120% of the rated output voltage), the protection function is triggered, shutting off
the output voltage. If this occurs, reset the S82H by turning it off for more than 1 minute and then turning it on again.
Output voltage (V)
Overvoltage
Approx. +20%
+10%
Rated output
voltage
–10%
Variable
Inrush Current, Rise Time, Hold Time
Input ON
Input OFF
AC input voltage
Inrush current when
input is turned ON
AC input current
Output voltage
Rise time
Output hold time
5