Communications, control systems, medical, instrumentation, defense and aerospace.
For details on proper operation please refer to the:
Design Guide & Applications Manual for Maxi, Mini, Micro Family.
Absolute Maximum Ratings
Product Overview
These DC-DC converter modules use
advanced power processing, control and
packaging technologies to provide the
performance, flexibility, reliability and cost
effectiveness of a mature power component.
High frequency ZCS/ZVS switching provides
high power density with low noise and
high efficiency.
Part Numbering
e.g. V150A24C500BL
V1 5 0 A
Product Grade Temperatures (°C)
Grade
Operating
Storage
E
=
- 10 to +100
- 20 to +125
C
=
- 20 to +100
- 40 to +125
T
=
- 40 to +100
- 40 to +125
H
=
- 40 to +100
- 55 to +125
M
=
- 55 to +100
- 65 to +125
B
Output Power
V
OUT
P
OUT
3.3V
200W, 264W
5V
300W, 400W
8V
300W, 400W
12V
400W, 500W
15V
400W, 500W
24V
400W, 500W
28V
400W, 500W
36V
400W, 500W
48V
400W, 500W
Pin Style
Finish
Blank:
Short
Tin/Lead
L:
Long
Tin/Lead
S:
Short ModuMate
Gold
N:
Long ModuMate
Gold
F:
Short RoHS
Gold
G:
Long RoHS
Gold
K:
Extra Long RoHS
Gold
Baseplate
Blank:
Slotted
2:
Threaded
3:
Through-hole
Output Voltage
3V 3
= 3.3V
5
= 5V
8
= 8V
12
= 12V
15
= 15V
24
= 24V
28
= 28V
36
= 36V
48
= 48V
150V Maxi Family
Page 1 of 13
Rev 2.7
02/2017
vicorpower.com
800 927.9474
150V Input
Module Family Electrical Characteristics
Electrical characteristics apply over the full operating range of input voltage, output load (resistive) and baseplate temperature, unless otherwise specified.
All temperatures refer to the operating temperature at the center of the baseplate.
MODULE INPUT SPECIFICATIONS
Parameter
Operating input voltage
Input surge withstand
Undervoltage turn-on
Undervoltage turn-off
Overvoltage turn-off/on
Disabled input current
81.9
201.9
97.0
84.9
210
220
1.1
Min
100
Typ
150
Max
200
250
99.0
Unit
V
DC
V
DC
V
DC
V
DC
V
DC
mA
PC pin low
<100ms
Notes
MODULE OUTPUT SPECIFICATIONS
Parameter
Output voltage setpoint
Line regulation
Temperature regulation
Power sharing accuracy
Programming range
10
±0.02
±0.002
±2
Min
Typ
Max
±1
±0.20
±0.005
±5
110
Unit
%
%
% / °C
%
%
Notes
Of nominal output voltage. Nominal input; full load; 25°C
Low line to high line; full load
Over operating temperature range
10 to 100% of full load
Of nominal output voltage. For trimming below 90%
of nominal, a minimum load of 10% of maximum
rated power may be required.
Externally applied
Externally applied
Externally applied
Externally applied
Externally applied
Externally applied
Externally applied
Externally applied
Externally applied
+OUT to –OUT, +Sense to –OUT — Absolute Maximum Ratings
3.3V
5V
8V
12V
15V
24V
28V
36V
48V
–0.5 to 4.7
–0.5 to 7.0
–0.5 to 10.9
–0.5 to 16.1
–0.5 to 20.0
–0.5 to 31.7
–0.5 to 36.9
–0.5 to 47.4
–0.5 to 62.9
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
Note:
The permissible load current must never be exceeded during normal, abnormal or test conditions. For additional output related application
information, please refer to output connections on page 8.
THERMAL RESISTANCE AND CAPACITY
Parameter
Baseplate to sink; flat, greased surface
Baseplate to sink; thermal pad (P/N 20263)
Baseplate to ambient
Baseplate to ambient; 1000LFM
Thermal capacity
Min
Typ
0.08
0.07
4.9
1.1
165
Max
Unit
°C/Watt
°C/Watt
°C/Watt
°C/Watt
Watt-sec/°C
150V Maxi Family
Page 2 of 13
Rev 2.7
02/2017
vicorpower.com
800 927.9474
150V Input
Module Family Electrical Characteristics (Cont.)
MODULE CONTROL SPECIFICATIONS
Parameter
Min
Typ
Max
Unit
Notes
Primary Side (PC = Primary Control; PR = Parallel)
PC bias voltage
current limit
PC module disable
PC module enable delay
PC module alarm
PC resistance
PR emitter amplitude
PR emitter current
PR receiver impedance
PR receiver threshold
PR drive capability
Secondary Side (SC = Secondary Control)
SC bandgap voltage
SC resistance
SC capacitance
SC module alarm
1.21
990
1.23
1000
0.033
0
1.25
1010
V
DC
Ω
µF
V
DC
With open trim; referenced to –Sense. See Fig. 7
Referenced to –Sense
0.9
5.7
150
375
2.4
500
2.5
625
2.6
12
1.0
5.9
5.50
1.5
2.3
5.75
2.1
2.6
4
6.00
3.0
2.9
7
0.5
1.1
6.1
V
DC
mA
V
DC
ms
Vavg
MΩ
Volts
mA
Ω
Volts
modules
25°C
Minimum pulse width: 20ns
Without PR buffer amplifier
UV, OV, OT, module fault. See Figs. 3 and 5
See Fig. 3, converter off or fault mode
PR load >30Ω, <30pF
PC current = 1.0mA
PC voltage = 5.5V
During normal operation
Switch must be able to sink
≥4mA.
See Fig. 2
MODULE GENERAL SPECIFICATIONS
Parameter
Remote sense (total drop)
Isolation test voltage (IN to OUT)*
Isolation test voltage (IN to base)*
Isolation test voltage (OUT to base)*
Isolation resistance
Weight (E, C, T grade)
Weight (H, M grade)
6.5
(184.3)
7.4
(209.3)
100
3000
1500
500
10
7.3
(207.5)
8.2
(232.5)
115
cURus, cTÜVus, CE
8.1
(230.7)
9.0
(255.7)
Min
Typ
Max
0.5
Unit
V
DC
V
RMS
V
RMS
V
RMS
MΩ
ounces
(grams)
ounces
(grams)
°C
See Figs. 3 and 5. Do not operate coverter >100°C.
UL60950-1, EN60950-1, CSA60950-1, IEC60950-1.
With appropriate fuse in series with the +Input
Notes
0.25V per leg (sense leads must be connected to
respective, output terminals)
Complies with reinforced insulation requirements
Complies with basic insulation requirements
Complies with operational insulation requirements
IN to OUT, IN to baseplate, OUT to baseplate
Temperature limiting
Agency approvals
* Isolation test voltage, 1 minute or less.
Note:
Specifications are subject to change without notice.
150V Maxi Family
Page 3 of 13
Rev 2.7
02/2017
vicorpower.com
800 927.9474
150V Input
MODULE SPECIFIC OPERATING SPECIFICATIONS
3.3V
OUT
, 264W (e.g. V150A3V3C264BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
78
4.14
Typ
80.8
80
4.3
7
±0.02
92
92
Max
100
4.46
8.3
±0.2
80
108
108
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
81.6
56
3.3V
OUT
, 200W (e.g. V150A3V3C200BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
81.2
4.14
Typ
82
164
4.3
6.4
±0.02
69.7
69.7
Max
205
4.46
7.5
±0.2
60.6
81.9
81.9
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
61.8
42.4
5V
OUT
, 400W (e.g. V150A5C400BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
83.9
6.03
Typ
84.9
75
6.25
11
±0.02
92
92
Max
94
6.47
12.9
±0.2
80
108
108
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
81.6
56
5V
OUT
, 300W (e.g. V150A5C300BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
83.6
6.03
Typ
84.9
150
6.25
7.7
±0.02
69
69
Max
188
6.47
10
±0.2
60
81
81
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
61.2
42
8V
OUT
, 400W (e.g. V150A8C400BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
83
9.36
Typ
84.2
320
9.7
11.4
±0.02
57.5
57.5
Max
400
10.1
12.5
±0.2
50
67.5
67.5
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
51
35
150V Maxi Family
Page 4 of 13
Rev 2.7
02/2017
vicorpower.com
800 927.9474
150V Input
MODULE SPECIFIC OPERATING SPECIFICATIONS (CONT.)
8V
OUT
, 300W (e.g. V150A8C300BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Output Current
Current limit
Short circuit current
Min
85
9.36
Typ
86.2
220
9.7
7.9
±0.02
43.1
43.1
Max
275
10.1
9.5
±0.2
37.5
50.7
50.7
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
38.2
26.2
12V
OUT
, 500W (e.g. V150A12C500BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
86.2
13.7
Typ
87.6
385
14.3
11.3
±0.02
48
48
Max
482
14.9
12.3
±0.2
41.67
56.3
56.3
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
42.5
29.1
12V
OUT
, 400W (e.g. V150A12C400BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
86.6
13.7
Typ
87.5
264
14.3
11
±0.02
38.3
38.3
Max
330
14.9
12.9
±0.2
33.33
45
45
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
33.9
23.3
15V
OUT
, 500W (e.g. V150A15C500BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
85
17.1
Typ
86.3
280
17.8
13.4
±0.02
38.3
38.3
Max
350
18.5
15
±0.2
33.33
45
45
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
33.9
23.3
15V
OUT
, 400W (e.g. V150A15C400BL)
Parameter
Efficiency
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load Current
Current limit
Short circuit current
Min
85
17.1
Typ
88.6
180
17.8
11.5
±0.02
30.7
30.7
Max
225
18.5
12.5
±0.2
26.67
36.1
36.1
Unit
%
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
3 A/D conversion register Here is an extract of some instructions of the source program that I downloaded from the Internet, which uses the PIC16F877 microcontroller chip (with Flash memory) to comple...
The understanding and questions about this solution are as follows. I hope everyone can discuss and learn together! Thank you! 1. Regarding the role of the MOS tube, what do you think the MOS tube is ...
Today I reviewed the expansion of RAM and ROM of 51 single-chip microcomputer, and gained a lot. I read a book about 51 several times before, but still didn't understand the timing of 51 accessing ext...
QT is a very good cross-platform tool. So we only need to master the method of QT to make the interface, and we can easily make QT cross-platform applications.Why should we learn QT_For_Android?1. Exp...
In recent years, the market for mobile/portable devices such as smartphones and laptops has continued to grow rapidly. While these products continue to integrate more new features to enhance the ...[Details]
1. Introduction
Light control circuit plays a vital role in urban street lamps or corridor lighting. With light control circuit, the lights can be automatically turned on and off according to ...[Details]
1 Introduction
In recent years, there have been many major advances in the production technology and processes of automotive headlights, which have greatly improved the performance of automoti...[Details]
Different initialization between C8051F and 80C51 series microcontrollers
In the past 30 years, major electronic component manufacturers in the world have launched their own unique single-chip...[Details]
Printed circuit boards ( PCBs
)
are used in most electrical products
. If a PCB has low
insulation resistance
(IR), the performance of the circuits on the PCB will be greatly reduced...[Details]
With concerns about the growing energy crisis, motor efficiency has become an important and timely topic. This is because motors use 63% to 70% of the electricity produced in the United States and ...[Details]
Motors are important products that convert electrical energy into mechanical energy to achieve automation, and they are widely used in industrial control, medical electronics, white a...[Details]
Currently, each country is developing its own USB interface
charging specifications
, which leads to a major problem that a USB interface
charging
device manufactured in one country...[Details]
With the rapid development of cities and the improvement of citizens' living standards, the number of various vehicles in cities is growing, and the demand for parking spaces in major commercial an...[Details]
Almost everyone in a student dormitory has a bedside lamp. But if you want to read for a while after turning off the lights and don't want to disturb your roommates' sleep, you may need a reading l...[Details]
The fluorescent lamps and energy-saving lamps we commonly use now have greatly improved luminous efficiency compared with the earlier ordinary incandescent lamps and have been widely used. With the...[Details]
Electric bicycles have long been a means of transportation for lower-income groups due to their affordability. The largest concentrated expense in the use of electric vehicles is the cost of replac...[Details]
Today, with the increasing integration of functions, mobile phones can also be used as portable media players (PMP), digital cameras, handheld computers (PDAs), and even global positioning systems (GP...[Details]
Leakage current is generated by parasitic resistance paths between the measurement circuit and a nearby voltage source. This current can significantly reduce the accuracy of low current measurement...[Details]
The biggest advantage of Profibus is that it is guaranteed by the stable international standard EN50170 and has been proven to be universal in practical applications. It has been widely used in man...[Details]