Wheelock
Buidi I lgent N etw orks
l ng nteli
ET Series
ET70SERIES
ET90SERIES
www.firecontrolinstruments.com
GENERAL
Wheelock has enhanced the ET Series
high-performance Speakers and Speaker
Strobe combinations. These speakers are
specifically designed to meet the critical
needs of the life safety industry for voice
and tone signaling. These dual voltage (25/
70 volt), multiple tap (from 1/8 to 8 watts)
audio systems now incorporate a new
low-profile design which results in more
space in standard electrical backboxes.
ET Series Speakers and Speaker Strobes
now incorporate a new speaker mounting
plate for faster and easier installation with
a built-in level adjustment feature, and a
new aesthetically pleasing two-screw grille
cover. Additionally, the ET Series Speaker
Strobe models now incorporate
the
new low-current, reduced-inrush,
Wheelock RSS Series Non-Sync/Sync
Strobes (synchronization of the strobe
flash is achieved when used with the
Wheelock SM or DSM Sync Module).
ET Series Speaker Strobes are designed
with maximum performance, reliability and
cost-effectiveness while meeting or ex-
ceeding the latest requirements of NFPA
72 (National Fire Alarm Code), ANSI 117.1
(American National Standard of Accessible
and Usable Buildings and Facilities), and
UL Standard 1971(Standard for Signaling
Devices for the Hearing Impaired). ET
Speaker Strobes, when properly specified
and installed in accordance with NFPA/
ANSI standards, can provide the equiva-
lent facilitation allowed under ADA Acces-
sibility Guidelines (ADAAG General Sec-
tion 2.2) by meeting or exceeding the il-
lumination which results from the ADA
specified strobe intensity of 75 candela at
50 feet (15.24 m). This is an illumination
of 0.030 lumens per square foot.
ET Series Speaker Strobes are UL listed
for indoor use, ceiling- and wall-mounting,
under Standard 1971 for Signaling Devices
for the Hearing Impaired and Standard 1480
for Speaker Appliances. They use a Xenon
flashtube with solid state circuitry enclosed
in a rugged LEXAN® lens to provide
maximum reliability for effective visual
signaling.
FEATURES
• Designed to meet or exceed NFPA/ANSI
Standard and ADA Accessibility Guide-
lines. Meets OSHA 29 Part 1910.165.
• High-efficiency speakers designed for
maximum output at minimum wattage
across 400 to 4,000 Hz frequency range.
• Field-selectable taps for 25 or 70 V
RMS
operation from 1/8 watt up to 8 watts in
3-dB steps.
• Sealed-back speaker construction
for extra protection and improved
audibility.
• Easy installation with In/Out screw
terminals using #12 AWG (3.25 mm²)
to #18 AWG (0.75 mm²) wiring.
• ET Series Speaker Strobe models are
available with the new RSS Series Non-
Sync/Sync Strobes in 15, 15/75, 30, 75,
and 110 candela for wall mounting; and
30, 75, and 100 candela for ceiling mount-
ing. When used in conjunction with
the Wheelock SM or DSM Sync Mod-
ules, these non-sync/sync strobes pro-
duce a synchronized strobe flash for
compliance with ADA guidelines con-
cerning photosensitive epilepsy.
• The 15/75 candela wall-mounted
strobes are listed at 15 candela under
UL standard 1971 and meet 75 candela
intensity on axis for ADA guidelines,
with low current draw.
• All strobe inputs compatible with stan-
dard reverse-polarity-type supervision of
circuit wiring by an alarm panel.
• The new speaker mounting plate
provides faster, easier installation in
attractive package styles for flush, semi-
flush, or surface mounting to standard
low-cost backboxes. Special slots are
provided for ease in leveling speaker and
speaker-strobe models.
• ET-1010 or ET-1080 Series models
available for vandal-resistant die-cast
speakers and speaker strobes.
ET90 Series
Speaker Strobe
ET70 Series
Speaker Strobe
S2652
(Speakers)
S2652/S5391
(Strobe/Speakers)
151-92-E
Vol. XXI
California
State Fire
Marshal
7135-0785:134
7125-0785:146
An ISO 9001 Company
.
LEXAN® is a registered trademark of GE Plastics, a subsidiary
of General Electric Company.
Specifications are provided for information only, and are
not intended to be used for installation purposes and are
believed to be accurate. However, no responsibility is
assumed by Fire Control Instruments for their use.
Specifications subject to change without notice.
© 2003
All Rights Reserved
9020-0579/Ver. 1.0
Page 1 of 4
A Honeywell Company
Buidi I lgent N etw orks
l ng nteli
ET Series
ST R O B E
N O N - YN C
S
ST R O B E
SY N C
ST R O B E
C A N D E LA
C O LO R
R ED
C O LO R
W HI E
T
FEATURES QUICK REFERENCE
M O D EL N U M B ER
ET70-
R
ET70-
W
ET90-
W
ET70- 415W - R
2
F
ET70- 41575W - R
2
F
ET70- 430W - R
2
F
ET70- 475W - R
2
F
ET70- 4110W - R
2
F
ET70- 4110W - W
2
F
ET90- 430C - W
2
F
ET90- 475C - W
2
F
ET90- 4100C - W
2
F
ET- 010-
1
R
ET- 010-
1
W
ET- 080-
1
R
ET- 080- S- 4- FR
1
L 2 V
ET- 080- L- FR
1
S V
ET- 080- SM - 4- FR
1
L 2 V
ET- 080- LM - 4- FR
1
S 2 V
ET- 080- S- 4- FR
1
M 2 V
ET- 080-S- 4- FR
1
I2 V
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
15
15
15/ 5
7
15/ 5
7
30
75
X
X
X
X
X
X
X
W A LL
MOUNT
C EI I G
LN
MOUNT
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
X
15
15/ 5
7
30
75
110
110
30
75
100
X
X
X
X
X
X
X
X
X
X
X
X
X
X
WIRING DIAGRAMS (all models)
ET Strobe devices synchronized
with multiple DSM Modules.
Interconnecting wiring shown.
Maximum of twenty (20) DSM Modules.
ET Speaker and Strobe operate
independently (non-sync or sync).
ET Strobe devices synchronized
with DSM Module dual Class “A” (Style Z) circuit
with NO audible silence feature.
For details on using SM or DSM Sync Modules,
refer to Wheelock data sheet #S3000,
or Wheelock installation instructions
P83123 (for SM) or P83177 (for DSM).
Specifications are provided for information only, and are not intended to be used for installation purposes and are believed to be accurate.
However, no responsibility is assumed by Fire Control Instruments for their use. Specifications subject to change without notice.
© 2003 All Rights Reserved
FIRE CONTROL INSTRUMENTS
16 Southwest Park, Westwood, MA 02090 USA • Tel: 781-471-3000 • Fax: 781-471-3099 • www.firecontrolinstruments.com
A Honeywell Company
9020-0579Ver. 1.0 / Page 2 of 4
Buidi I lgent N etw orks
l ng nteli
ET Series
Contact Wheelock for installation instructions (Wheelock P83567) and general information sheet (Wheelock P82380) for these products.
These materials undergo periodic changes. It is important that you have current information on these products. These materials contain
important information that should be read prior to specifying or installing these products, including:
• Total current required by all devices connected to system primary and secondary power sources.
• Fuse ratings on NAC circuits to handle maximum inrush or peak currents from all devices on those circuits.
• Composite flash rate from multiple strobes within a person’s field of view.
• Voltage applied: the voltage applied to these products must be within their rated input voltage range.
• Installation of 110/100 candela strobe products in sleeping areas.
• Installation in office areas and other specification and installation issues.
• Note: Use strobes only on circuits with continuously applied operating voltage. Do not use strobe on coded or interrupted
nac circuits in which the applied voltage is cycled on and off, as the strobe may not flash.
• Conductor specifications: Conductor size (AWG), length and capacity should be taken into consideration prior to design and
installation of these products, particularly in retrofit installations.
FAILURE TO COMPLY WITH THE INSTALLATION INSTRUCTIONS OR GENERAL INFORMATION SHEETS COULD RESULT IN
IMPROPER INSTALLATION, APPLICATION, AND/OR OPERATION OF THESE PRODUCTS IN AN EMERGENCY SITUATION, WHICH
COULD RESULT IN PROPERTY DAMAGE AND SERIOUS INJURY OR DEATH TO YOU AND/OR OTHERS.
Wheelock products must be used within their published specifications and must be
PROPERLY
specified, applied, installed, operated,
maintained, and operationally tested in accordance with their installation instructions at the time of installation and at least twice a year
or more often and in accordance with local, state, and federal codes, regulations, and laws. Specification, application, installation,
operation, maintenance, and testing must be performed by qualified personnel for proper operation in accordance with all of the latest
National Fire Protection Association (NFPA), Underwriters’ Laboratories (UL), National Electrical Code (NEC), Occupational Safety and
Health Administration (OSHA), local, state, county, province, district, federal, and other applicable building and fire standards, guide-
lines, regulations, laws, and codes including, but not limited to, all appendices and amendments and the requirements of the local
authority having jurisdiction (AHJ).
ARCHITECT & ENGINEER SPECIFICATIONS
The speaker appliances shall be Wheelock ET Series Speakers and Speaker Strobes or approved equivalent. The speakers shall
be listed under Standard UL 1480 for Fire Protective Service. Speaker appliances equipped with strobes shall additionally be Listed
under UL 1971, Signaling Devices for the Hearing Impaired.
All speakers shall include both 25 and 70 V
RMS
inputs with field-selectable power taps from 1/8 watt to 8 watts with listed sound
output up to 94 dBA for speakers and speaker-strobes. Strobes shall be Listed for 20 to 31 VDC input using filtered power or unfil-
tered power supply V
RMS
. All models shall have provisions for standard reverse-polarity-type supervision for strobe portion and In/
Out field wiring using terminals that accept #12 AWG (3.25 mm²) to #18 AWG (0.75 mm²) wiring. Additionally, the speaker shall
incorporate sealed-back construction.
Combination speaker-strobe appliances shall incorporate a Xenon flashtube enclosed in a rugged LEXAN® lens or equivalent with
solid state circuitry. Strobe shall meet UL 1971 and produce a flash rate of one (1) flash per second minimum over the listed input
voltage (20 - 31 VDC) range. The strobe intensity shall be rated per UL 1971 for 15, 15/75, 30, 75, or 110 candela for wall mounting;
and 15, 30, 75, or 100 candela for ceiling-mount applications. The 15/75 candela wall strobe shall be specified when 15 candela UL
1971 listing with 75 candela intensity on-axis is required.
Combination speaker-strobe appliances shall incorporate the Wheelock RSS Series Non-Sync/Sync circuitry and shall be designed
for compatibility with Wheelock SM and DSM Sync Modules for synchronized strobe flash. Wheelock Sync Modules and Synchronized
Strobes shall be designed as a system for continuous activation of the strobes; should the Sync Module contacts fail in the passive
state (i.e., contacts remain closed), the strobes shall revert to a non-synchronized rate of 1 flash per second (default mode).
All UL 1971 listed strobe appliances shall be certified to meet FCC Part 15, Class B and incorporate low temperature compensation
to ensure the lowest possible current consumption. Strobe activation shall be via independent input from the audio circuit.
The speakers and speaker-strobe appliances shall be designated for indoor surface or flush mounting. The speaker and speaker
strobes shall incorporate a speaker mounting plate with a grille cover which is secured with two screws for a level, aesthetically
pleasing finish. They shall mount on standard electrical hardware requiring no additional trim plate or adapter. The appliance shall be
finished in a textured red or white color.
Specifications are provided for information only, and are not intended to be used for installation purposes and are believed to be accurate.
However, no responsibility is assumed by Fire Control Instruments for their use. Specifications subject to change without notice.
© 2003 All Rights Reserved
FIRE CONTROL INSTRUMENTS
16 Southwest Park, Westwood, MA 02090 USA • Tel: 781-471-3000 • Fax: 781-471-3099 • www.firecontrolinstruments.com
A Honeywell Company
9020-0579/Ver. 1.0 / Page 3 of 4
GENERAL NOTES
• Strobes are designed to flash at 1 flash per second minimum
from 20 to 31 VDC. Note that NFPA-72 (1996) specifies a flash
rate of 1 to 2 flashes per second, and ADA guidelines specify
a flash rate of 1 to 3 flashes per second.
• All candela ratings represent minimum effective strobe inten-
sity based on UL 1971.
• Series ET70 and ET90 Speaker Strobe products are
listed under UL 1971 for indoor use with a tempera-
ture range of 32°F to 120°F (0°C to 49°C) and maxi-
mum humidity of 85%. Series ET-1010 Speakers
(without strobes) are listed for indoor/outdoor use
with a temperature range of -31°F to 150°F (-35°C
to 66°C) and maximum humidity of 95%. ET-1080
Speaker Strobes are listed for indoor use with a
temperature range of 32°F to 120°F (0°C to 49°C).
Speaker dB at 10 f .( . 48 m ) ( ated W atts)
t 30
R
1/
8
78.
3
1/
4
81.
5
1/
2
84.
4
1
87.
2
2
90.
1
4
92.
8
8
94.
9
N O TE:
Sl hti c eas i dB on N on- tobe Speaker .
i nr e n
g
Sr
s
ORDERING INFORMATION
M O D EL N U M B ER
ST R O B E
C A N D E LA
—
—
—
15
15/75
30
75
110
110
30
75
100
I P U T V O LTA G E
N
12 VD C /24 VD C
12 VD C /24 VD C
A V G . ST R O B E
*
C U R R E N T ( M P S) @
A
24 V D C
—
—
—
0.050
0.065
0.081
0.133
0.161
0.161
0.102
0.204
0.238
A V G .C U R R E N T
0. 14 ( 2)/0. 25 ( 4)
0
1
0
2
0. 20 ( 2)/0. 38 ( 4)
0
1
0
2
E,N
W
M O U N T I G O PT I N S
N
O
**
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
E, L, N, O, P, Q, V, Y Z
,
SP E A K E R S
W al- ount or
lM
C eii g- ount
ln M
ET70-R
ET70-W
ET90-W
ET70-2415W-FR
ET70-241575W-FR
SP E A K E R
ST R O B E S
W al- ount
lM
ET70-2430W-FR
ET70-2475W-FR
ET70-24110W-FR
ET70-24110W-FW
ET90-2430C-FW
ET90-2475C-FW
ET90-24100C-FW
SM - 2/ 4-
1 2 R
D SM - 2/ 4-
1 2 R
SP E A K E R
ST R O B E S
C eii g- ount
ln M
SY N C
M O D U LE S***
NOTES: 1)
ET90 MODELS
with and without strobes are offered in white only.
2)
SUFFIXES USED ABOVE:
W = Wall mounting;
C = Ceiling mounting; F = Fire lettering; R at end = Red; W at end = White.
EXAMPLES:
ET70-R (Red); ET70-2415W-FR (Wall
mounting – Fire lettering, Red); ET90-2475C-FW (Ceiling mounting – Fire lettering; White).
3)
FREQUENCY RANGE
of speakers is 400
to 4,000 Hz.
4)
A 10 µF BLOCKING CAPACITOR
for DC supervision of audio lines by the FACP is factory-wired in series with
the speaker input.
5)
dBA
is rated per UL 1480.
*
Average current
per actual Wheelock production testing 24 VDC nominal voltage. For rated average, peak and inrush cur-
rents across the listed voltage ranges for both filtered DC and unfiltered V
RMS
(or on models below, full-wave-rectified), see
the installation instructions for this product series (Wheelock P83567).
** For descriptions of
MOUNTING OPTIONS,
refer to Notifier Data Sheet DN-6111, derived from Wheelock S7000.
***
SM Sync Modules
are rated for 3.0 amperes at 12/24 VDC;
DSM Dual Control Modules
are rated for 3.0 amperes per
circuit. The maximum number of interconnected DSM modules is twenty (20). Refer to installation instructions for SM (Wheelock
P83123) and DSM (Wheelock P83177).
M O D EL N U M B ER
ET- 010-
1
R
ET- 010-
1
W
ET- 080-
1
R
ET- 080- S- 4- FR
1
L 2 V
ET- 080- L- FR
1
S V
ET- 080- SM - 4- FR
1
L 2 V
ET- 080- LM - FR
1
S V
ET- 080- S- 4- FR
1
M 2 V
ET- 080-S- 4- FR
1
I 2 V
ST R O B E
C A N D E LA
—
—
—
15
15
15/ 5
7
15/ 5
7
30
75
dB A @ 10
FT.
( . 48 m )
30
78 -96
78 -96
78 -96
78 -96
78 -96
78 -96
78 -96
78 -96
78 -96
A V G . ST R O B E
*
C U R R EN T
( M P S) @ 24
A
VD C
—
—
—
0. 74
0
0. 96
0
0. 00
1
0. 38
1
0. 24
1
0. 00
2
M O U N TI G
N
O P T I N S**
O
E,K ,N ,R,S,T,U ,Z
E,K ,N ,R,S,T,U ,Z
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
E,L,N ,O ,P Q ,V,Y,Z
,
SP E A K E R S
D i - as
eC t
SP E A K E R
ST R O B E
S
D i - as
eC t
T hese m odel al o ut lze t e SM and D SM Sync M odul s,see previ us t bl .
s s
ii
h
e
o
a e
NOTES PARTICULAR TO TABLE ABOVE: 1)
ET-1010/1080 MODELS
can be used with Wheelock Model RSSP-24110W-FR
strobe/plate assembly for 110 candela wall speaker strobes.
2)
SUFFIXES USED ABOVE:
V = Vertical lens; C = Ceiling lens; F =
Fire lettering; R = Red plate; W = White plate.
The letters SL and SLM denote synchronized products.
3)
FIELD-SELECT-
ABLE TAPS
for above models: 1/8, 1/4, 1/2, 1, 2, 4 or 8 watt operation (4-watt tap not available with 25 V
RMS