Data are valid at +25°C, unless otherwise specified.
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent input
voltage range
Transient input voltage
Undervoltage lock-out
(UVLO)
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Full temperature range
Ui min. to max.
75% load
Ambient temperature : +25°c
Ui nominal, 75% load
Full temperature range
Ui min. to max.
Full temperature range
Ui min. to max.
Nominal
Nominal
Nominal
Nominal
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Maximum
Maximum
VDC
VDC
VDC
VDC
%
W
A
A
A
A
mVpp
mVpp
mVpp
%
%
%
µF
µF
1.000
330
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
40
50
60
+/- 1
+/- 2,5
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
40
50
60
+/- 1
+/- 2,5
See on page 6
1.000
330
Conditions
Limit or
typical
Nominal
Min. - Max.
Min. - Max.
Maximum
Minimum
Maximum
Maximum
Maximum
Maximum
Maximum
Units
Hi-Rel
Grade
Single Output MGDS-10
10-C
5
4,5-5,5
/
/
4
4,3
30
50
50
50
10 - H
20
9-36
/
40/0,1
7
8,5
30
50
30
30
10 - J
28
16-40
16-45
50/0,1
12
15
30
30
30
30
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load (Consult factory)
turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
VDC
VDC
VDC
VDC/S
VDC
VDC
ms
mApp
mA
mA
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
40
50
60
+/- 1
+/- 2,5
4
Set Point accuracy
Output power
Output current **
3,3V output
5V output
12V output
15V outputt
Ripple output voltage ***
3,3V and 5V output
12V output
15V output
Line regulation
Load regulation ****
Efficiency
Maximum admissible
Capacity load
3,3V and 5V output
12V and 15V output
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
1.000
330
Note * : For proper operation the MGDM-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note*** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/rated voltage depending on isolation requirement) connected between the pin Gin and the
pin Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note**** : For load regulation characteristics from 0% to full load, please see page 6.
Data are valid at +25°C, unless otherwise specified.
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent input
voltage range
Transient input voltage
Undervoltage lock-out
(UVLO)
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Full temperature range
Ui min. to max.
75% load
Ambient temperature : +25°c
Ui nominal, 75% load
Full temperature range
Ui min. to max.
Full temperature range
Ui min. to max.
Nominal
Nominal
Nominal
Nominal
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Maximum
Maximum
VDC
VDC
VDC
VDC
%
W
A
A
A
A
mVpp
mVpp
mVpp
%
%
%
%
µF
µF
470
100
+/- 5
+/- 12
+/- 15
/
+/- 2
+/- 5
+/- 1
+/- 0,40
+/- 0,33
/
40
50
60
+/- 1
+/- 2,5
+/- 0,5
+/- 5
+/- 12
+/- 15
/
+/- 2
+/- 5
+/- 1
+/-0, 40
+/- 0,33
/
40
50
60
+/- 1
+/- 2,5
+/- 0,5
See on page 6
470
100
Conditions
Limit or
typical
Nominal
Min. - Max.
Min. - Max.
Maximum
Minimum
Maximum
Maximum
Maximum
Maximum
Maximum
Units
Hi-Rel
Grade
Bi Output MGDB-10
10-C
5
4,5-5,5
/
/
4
4,3
30
50
50
50
10 - H
20
9-36
/
40/0,1
7
8,5
30
50
30
30
10 - J
28
16-40
16-45
50/0,1
12
15
30
30
30
30
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load (Consult factory)
Turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
VDC
VDC
VDC
VDC/S
VDC
VDC
ms
mApp
mA
mA
+/- 5
+/- 12
+/- 15
+/- 24
+/- 2
+/- 5
+/- 1
+/-0, 40
+/- 0,33
+/-0,20
40
50
60
+/- 1
+/- 2,5
+/- 0,5
4
Set Point accuracy
Output power
Output current **
5V output
12V output
15V output
24V output
Ripple output voltage ***
5V output
12V output
15V and 24 output
Line regulation
Load regulation ****
Cross load output
regulation
Efficiency
Maximum admissible
Capacity load
5V output
12V, 15V and 24V output
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
+ Vout nominal load
- Vout from 25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
470
100
Note * : For proper operation the MGDM-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note*** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/rated voltage depending on isolation requirement) connected between the pin Gin and the
pin Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note**** : For load regulation characteristics from 0% to full load, please see page 6.
Data are valid at +25°C, unless otherwise specified.
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent input
voltage range
Transient input voltage
Undervoltage lock-out
(UVLO)
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Set Point accuracy
Output power
Output current **
5 & +/- 12V output
5 & +/- 15V output
Ripple output voltage ***
5V output
12V output
15V output
Line regulation
Load regulation ****
Cross load output
regulation
Efficiency
Maximum admissible
Capacity load
5V output
12V and 15V output
Full temperature range
Ui min. to max.
75% load
Ambient temperature : +25°c
Ui nominal, 75% load
Full temperature range
Ui min. to max.
Full temperature range
Ui min. to max.
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
+ Vout nominal load
- Vout from 25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
Nominal
Nominal
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Maximum
Maximum
VDC
VDC
%
W
A
A
mVpp
mVpp
mVpp
%
%
%
%
µF
µF
5 & +/- 12
5 & +/- 15
+/- 2
5 & +/- 2,5
1 & +/- 0,20
1 & +/- 0,15
40
50
60
+/- 1
+/- 2,5
+/- 0,5
82
470
100
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load
Turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
Nominal
Min. - Max.
Min. - Max.
Maximum
Minimum
Maximum
Maximum
Maximum
Maximum
Maximum
VDC
VDC
VDC
VDC/S
VDC
VDC
ms
mApp
mA
mA
20
9-36
/
40/0,1
7
8,5
30
50
30
30
Conditions
Limit or
typical
Units
Hi-Rel
Grade
Tri Output MGDT-10
10 - H
10 - J
28
16-40
16-45
50/0,1
12
15
30
30
30
30
5 & +/- 12
5 & +/- 15
+/- 2
5 & +/- 2,5
1 & +/- 0,20
1 & +/- 0,15
40
50
60
+/- 1
+/- 2,5
+/- 0,5
82
470
100
4
Note * : For proper operation the MGDM-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note*** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/rated voltage depending on isolation requirement) connected between the pin Gin and the
pin Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note**** : For load regulation characteristics from 0% to full load, please see page 6.
I have read many articles about Zigbee on the Internet, with mixed reviews. Some say it is the development direction of the next generation of wireless industry, while others say it has poor wall pene...
Imagine driving to work this morning: the traffic light turns green, you immediately step on the accelerator, and the car responds quickly within a few seconds and continues to drive to work. This pro...
The competent departments of information industry in all provinces, autonomous regions, municipalities directly under the Central Government and cities with independent planning status:According to th...
Write a simple driver mydriver.dll under wince5.0. When loading the module, the following appears: ... 4294769776 PID:3f96bca TID:3fa0f9a 0x83fca800: >>> Loading module mydriver.dll at address 0x03010...
As the title says, I solved the problem of how to prevent the messagebox from being covered yesterday. Today I encountered the problem that after the messagebox prompt box appears, I can still operate...
How to change the sound of clicking the screen in EVC by modifying the program. I modified the registry, but it didn't work. . The code is as follows. HKEY hKey1; DWORD dwType1; DWORD dwScreen1 = 1; D...
Traditional broadcasting systems generally need to be operated manually at a fixed time, and can only realize one-way broadcasting with few functions. Traditional bell ringing equipment has a singl...[Details]
1. Circuit composition
The whole circuit consists of two parts:
1. Power saving control circuit
As shown in the figure below. Including delay circuit and drive circuit.
(1) Delay ci...[Details]
1. Introduction
With the growth of parking demand, the scale of parking lots is becoming larger and larger. A lot of research has been done on intelligent parking lots in China, but most of th...[Details]
Converged processors meet scalability requirements
In current embedded system design, solutions based on MCU, DSP, FPGA and ASIC account for more than 90% of the market share. These solutions ...[Details]
The Portable Digital Data Acquisition System (PDDAS) uses LabVIEW Real-Time and PXI to control the wind tunnel test and record air pressure data from 128 different channels.
"The LabVIEW Real-...[Details]
To differentiate their products in a crowded and competitive market, manufacturers of handheld devices often consider battery life and power management as key selling points for cell phones, PDAs, ...[Details]
July 11, 2012, Beijing - Altera Corporation (NASDAQ: ALTR) today announced the launch of 40-Gbps Ethernet (40GbE) and 100-Gbps Ethernet (100GbE) intellectual property (IP) core products. These core...[Details]
Images in science fiction movies often break through the limits of reality, such as in the movie "Minority Report." Tom Cruise uses a multi-touch screen to browse information. Capacitive sensing te...[Details]
1. Introduction
With the gradual automation and modernization of industrial control systems, fieldbus control systems have received more and more attention and application. CAN bus is currentl...[Details]
1 Introduction
The Third Steel Plant of Jigang Group is a key investment project of Jigang Group during the "15th Five-Year Plan". It has introduced first-class domestic and foreign advanced eq...[Details]
Xiaomi, a well-known Internet phone in mainland China, won a million-unit order contract from China Unicom on November 20 last year, which made Xiaomi famous in mainland China. In April this year...[Details]
LED lamps and bulbs are now rapidly replacing incandescent, halogen and CFL (compact fluorescent lamp) light sources in many general lighting applications. Flyback DC/DC converters are the power su...[Details]
In the single-chip microcomputer system, in addition to display devices, sound devices are often used, and the most common sound device is the buzzer. Buzzers are generally used for some low-demand...[Details]
The TPS92210 is a single-stage LED lighting pulse width modulation (PWM) controller. The TRIAC dimmable solution not only regulates the LED current, but also achieves a power factor close to 1. The...[Details]
At present, how various communication technologies will evolve after 3G is a focus of great concern in the industry. Especially for TD-SCDMA, whether it can achieve smooth evolution to the next gen...[Details]