High Speed Fuses
Square Body DIN 43 653 — 1250V/1300V (IEC/UL):
50-1400A
1250V/1300V (IEC/UL) 50-1400A
Specifications
Description:
Square body DIN
43 653 stud-mount high speed
fuses.
Dimensions:
See dimensions
illustration.
Ratings:
Volts: — 1250Vac (IEC)
— 1300Vac (UL)
Amps: — 50-1400A
IR: — 100kA RMS Sym.
Ag ency Information:
CE, Designed and tested to IEC
60269: Part 4, UL Recognized. Consult Cooper Bussmann
for UL Recognition/CSA Component Acceptance status.
Electrical Characteristics
Total Clearing I
2
t
1.5
K
1.25
1.0
Arc Voltage
This curve gives the peak
1.8
arc voltage, UL, which
1.4
may appear across the
fuse during its operation
10
3
8
as a function of the
applied working voltage,
6
Eg, (rms) at a power factor
5
4
of 15%.
3
3
2.5
UL
E
g
600
800
1000 1200 1400
Power Losses
Watts loss at rated current
is given in the electrical
characteristics. The curve
allows the calculation of
the power losses at load
currents lower than the
rated current. The
correction factor, Kp, is
given as a function of the
RMS load current, Ib, in %
of the rated current.
400
1.0
K
p
0.8
0.6
0.5
0.4
0.3
0.2
The total clearing I
2
t at
rated voltage and at
power factor of 15% are
0.5
given in the electrical
0.4
characteristics. For other
0.3
voltages, the clearing I
2
t
is found by multiplying by
0.2
E
g
correction factor, K,
400 600 800 1000 1200 1400
given as a function of
Dashed lines (- - - - - -) apply to the following
applied working voltage,
amperages:.
Eg, (rms).
Size
Amps.
1*
1
2
3
400A
500-630A
630-1000A
800-1400A
0.1
30 40 50
60
70
I
b
80 90 100%
Features and Benefits
• Excellent DC performance
• Low arc voltage and low energy let-through (I
2
t)
• Low watts loss
• Superior cycling capability
Typical Applications
• DC common bus
• DC drives
• Power converters/rectifiers
• Reduced voltage starters
For Other Voltage Ratings in This Body Style
• See pages 122 (690V/700V) and 146 (1000V)
Dimensions (mm)
Type -KN/110
H
20
25
25
30
108
A
Dimensions (mm)
Type -/110, -TN/110
Siz e
1*
1
2
3
A
80
80
80
81
B
138
138
138
139
D**
58
66
75
90
E
45
53
61
76
Siz e
1*
1
2
3
A
80
80
80
81
B
138
138
138
139
D
58
66
75
90
E
45
53
61
76
C
H
20
25
25
30
1mm = 0.0394” / 1” = 25.4mm
**Microswitch.
1mm = 0.0394” / 1” = 25.4mm
H
11
D
E
B
D
11
A
H
6
E
E
B
6
E
160
For product data sheets, visit www.cooperbussmann.com/datasheets/ulcsa
High Speed Fuses
Square Body DIN 43 653 — 1250V/1300V (IEC/UL):
50-1400A
Catalog Numbers
Catalog Numbers
-TN/110
-/110
Type T
Visual
Indicator
Indicator
for Micro
170M3138
170M3188
170M3139
170M3189
170M3140
170M3190
170M3141
170M3191
170M3142
170M3192
170M3143
170M3193
170M3144
170M3194
170M3145
170M3195
170M3146
170M3196
170M3147
170M3197
170M3148
170M3198
170M4138
170M4188
170M4139
170M4189
170M4140
170M4190
170M4141
170M4191
170M4142
170M4192
170M4143
170M4193
170M4144
170M4194
170M4145
170M4195
170M4146
170M4196
170M4147
170M4197
170M5138
170M5188
170M5139
170M5189
170M5140
170M5190
170M5141
170M5191
170M5142
170M5192
170M5143
170M5193
170M5144
170M5194
170M5145
170M5195
170M5146
170M5196
170M5147
170M5197
170M5148
170M5198
170M5149
170M5199
170M5150
170M5200
170M6138
170M6188
170M6139
170M6189
170M6140
170M6190
170M6141
170M6191
170M6142
170M6192
170M6143
170M6193
170M6144
170M6194
170M6145
170M6195
170M6146
170M6196
170M6147
170M6197
170M6148
170M6198
170M6149
170M6199
170M6150
170M6200
170M6151
170M6201
-KN/110
Type K
Indicator
for Micro
170M3238
170M3239
170M3240
170M3241
170M3242
170M3243
170M3244
170M3245
170M3246
170M3247
170M3248
170M4238
170M4239
170M4240
170M4241
170M4242
170M4243
170M4244
170M4245
170M4246
170M4247
170M5238
170M5239
170M5240
170M5241
170M5242
170M5243
170M5244
170M5245
170M5246
170M5247
170M5248
170M5249
170M5250
170M6238
170M6239
170M6240
170M6241
170M6242
170M6243
170M6244
170M6245
170M6246
170M6247
170M6248
170M6249
170M6250
170M6251
Rated
Current
RMS-Amps
50
63
80
100
125
160
200
250
315
350
400
160
200
250
315
350
400
450
500
550
630†
250
280
315
350
400
450
500
550
630
700
800
900†
1000†
315
350
400
450
500
550
630
700
800‡
900‡
1000‡
1100‡
1250†
1400†
Electrical Characteristics
I
2
t (A
2
Sec)
Clearing
Clearing
Pre-arc
at 1000V
at 1250V
135
815
1100
215
1300
1750
420
2500
3350
750
4450
5950
1450
9000
11500
2600
16000
21000
5150
31000
41000
9200
54500
73000
18500
115000
150000
27000
165000
220000
53000
265000
335000
1900
11500
15500
3800
22500
30000
7750
46000
61500
15000
90000
120000
20000
125000
165000
29500
175000
235000
42000
250000
335000
69500
340000
435000
95000
465000
590000
130000
660000
6500
38500
51500
9350
55500
74500
13000
77500
105000
16500
97500
135000
23000
140000
180000
34000
205000
270000
48000
285000
380000
62000
370000
495000
115000
575000
730000
160000
795000
1050000
245000
1200000
1550000
360000
1750000
480000
2350000
9500
58000
77500
13500
81500
110000
19500
120000
160000
31000
185000
245000
39000
235000
310000
55000
325000
435000
83500
495000
665000
115000
705000
940000
205000
995000
1300000
305000
1500000
1900000
450000
2150000
2750000
575000
2800000
3600000
810000
3950000
1250000
6000000
Siz e
1*
1
2
3
Watts
Loss
15
20
25
30
35
40
45
55
60
65
70
45
50
60
65
70
75
80
85
95
100
65
70
75
80
85
90
95
100
110
115
120
125
135
85
90
95
100
105
110
115
120
125
130
135
140
145
150
High Speed
Fuses
†Rated voltage (IEC) 1100V.
‡Rated voltage (IEC) 1250V.
• Watts loss provided at rated current.
• Microswitch indicator ordered separately. See accessories on pages 185-186.
• For fuse curves see pages 166 and 167.
For product data sheets, visit www.cooperbussmann.com/datasheets/ulcsa
161