Icu 25 kA at 220...240 V AC 50/60 Hz conforming to IEC 60947-2
Icu 14 kA at 500...525 V AC 50/60 Hz conforming to IEC 60947-2
18 kA at 480Y/277 V AC 50/60 Hz conforming to UL 489
14 kA at 600Y/347 V AC 50/60 Hz conforming to UL 489
25 kA at 208Y/120 V AC 50/60 Hz conforming to UL 489
Icu 18 kA at 380...415 V AC 50/60 Hz conforming to IEC 60947-2
Icu 18 kA at 440 V AC 50/60 Hz conforming to IEC 60947-2
690 V AC 50/60 Hz conforming to IEC 60947-2
25 kA at 220...240 V AC 50/60 Hz conforming to IEC 60947-2
14 kA at 500...525 V AC 50/60 Hz conforming to IEC 60947-2
18 kA at 380...415 V AC 50/60 Hz conforming to IEC 60947-2
18 kA at 440 V AC 50/60 Hz conforming to IEC 60947-2
8 kV conforming to IEC 60947-2
1
[Ue] rated operational voltage
[Ics] rated service breaking capacity
[Uimp] rated impulse withstand voltage
Aug 16, 2019
Disclaimer: This documentation is not intended as a substitute for and is not to be used for determining suitability or reliability of these products for specific user applications
[Ui] rated insulation voltage
Trip unit technology
Trip unit name
Trip unit protection functions
Protection type
Trip unit rating
Magnetic hold current
Magnetic tripping current
Suitability for isolation
Utilisation category
Mechanical durability
Electrical durability
Connection pitch
Local signalling
Toggle padlocking (with accessories)
Connections - terminals
Thread type
Thickness
Tightening torque
Number of slots
Power wire stripping length
Quality labels
Standards
800 V conforming to IEC 60947-2
Thermal-magnetic
TM-D
LI
Overload protection (thermal)
Short-circuit protection (magnetic)
90 A at 40 °C
1000 A
1500 A
Yes conforming to IEC 60947-2
Category A
15000 cycles conforming to IEC 947-1 Annex K ed 5.2
10000 cycles conforming to IEC 947-1 Annex K ed 5.2 for In at 440 V
27 mm
Presence of auxiliary contacts: flag (green)
Padlock in OFF or ON position
Upside compression lug/busbar
Downside compression lug/busbar
M6
6.5 mm
5 N.m for 2.5…16 mm² (AWG 14...AWG 4)
9 N.m for 25…95 mm² (AWG 3...AWG 3/0)
1 slot(s) for auxiliary switch OF (plug-in)
1 slot(s) for voltage release MN or MX (plug-in)
20 mm
CE
NMX J-266
NEMA AB1
EN/IEC 60947-2
CSA C22.2 No 5
UL 489
EN/IEC 60947-5-1
GB 14048.2
Grey (RAL 7016)
6
137 mm
54 mm
80 mm
0.669 kg
Set of 1
Colour
9 mm pitches
Height
Width
Depth
Net weight
Quantity per set
Environment
Product certifications
UL
IEC
CCC
EAC
CSA
NOM
Front cover: IP40 conforming to IEC 60529
IK07 conforming to IEC 62262
3 conforming to IEC 60947-1
-25…70 °C
-50…85 °C
2000 m without derating
5000 m with derating
IP degree of protection
IK degree of protection
Pollution degree
Ambient air temperature for operation
Ambient air temperature for storage
Operating altitude
2
Offer Sustainability
Sustainable offer status
REACh Regulation
EU RoHS Directive
Mercury free
RoHS exemption information
China RoHS Regulation
Environmental Disclosure
Circularity Profile
WEEE
Green Premium product
REACh Declaration
Pro-active compliance (Product out of EU RoHS legal scope)
EU RoHS Declaration
Yes
Yes
Download RoHS China Declaration
Product out of China RoHS scope. Substance declaration for your information
Product Environmental Profile
No need of specific recycling operations
The product must be disposed on European Union markets following specific waste collection and