SeriesOneDR Timer
• 6 Amp AC and DC Rated output
• Compact Size (11mm wide)
• Dual SCR or MOSFET output
• AC/DC control
• Zero-crossing (resistive loads) or random-fire (inductive loads) AC output
• Timer Status LED Indicator
• UL Listed, HP rated
• 8 Industry standard functions (A/At, B, C, D/Di, H/Ht, L/Li, Ac and Bw)
PRODUCT SELECTION
Control Voltage
12-24 VAC/DC
90-140 VAC/DC
180-280 VAC/DC
AC output
DRTx24D06x
DRTx24B06x
DRTx24A06x
DC Output
DRTx06D06
AVAILABLE OPTIONS
OUTPUT SPECIFICATIONS (1)
Description
Operating Voltage
Transient Overvoltage [Vpk] @ 25°C
Rated Load Current (2)
Rated Load Current {UL508 Motor Controller} (2) [Arms]
Minimum Load Current
Maximum Off-State Leakage Current @ Rated Voltage
Minimum Off-State dv/dt @ Maximum Rated Voltage [V/µsec] (3)
Maximum Surge Current (AC output 1 cycle. DC output 10ms)
Maximum I²t for Fusing [A² sec]
Maximum On-State Voltage Drop @ Rated Current [Vpk]
Maximum On-State Resistance (RDS-ON) [Ohms]
HP rating UL 508/IEC60947[HP (KW)]: 240 VAC
IEC 62314 LC-A [FLA]
IEC 62314 LC-B [Kw]
Wire Size min/max (solid/stranded) [AWG/ IEC mm²] (4)
Output Terminal Screw Torque [in lb (Nm)]
DRTx24
24-280 VAC (47-440Hz)
600
6 Arms
3.6 Arms
150 mArms
0.1 mArms
500
285/300 Apk (50/60Hz)
410/375 (50/60Hz)
1.3
NA
1/3 (0.24)
6A
1.44
22/12 [0.33/3.31]
7.0 (0.8)
DRTx06
1-48 Vdc
60 Vdc
6A
NA
100 mA
20 µA
NA
60 A
NA
0.3 Vdc
0.034
NA
NA
NA
22/12 [0.33/3.31]
7.0 (0.8)
INPUT SPECIFICATIONS (1)
Description
Control Voltage Range
Must Turn-Off Voltage
Min Input Current @ Min Voltage (AC/DC) (for on-state)
Maximum Input Current @ Maximum Voltage
Nominal Input Impedance
Wire Size min-max (solid/stranded) [AWG/ IEC mm²] (4)
LED Status Indicator (Color)
Input Terminal Screw Torque [in lb (Nm)]
DRTxxxD06
12-24 VAC/DC
1 VAC/DC
7.6/6.3 mA (5)
12.1/9.1 mA (6)
2K (7)
22-16 / 0.33-1.31
Yes (green)
4.4 (0.5)
DRTx24A06
180-280 VAC/DC
20 VAC/DC
7.2/7.1 mA
9.7/9.6 mA
25K
22-16 / 0.33-1.31
Yes (green)
4.4 (0.5)
DRTx24B06
90-140 VAC/DC
10 VAC/DC
7.6/7.4 mA
12.5/12.3 mA
12K
22-16 / 0.33-1.31
Yes (green)
4.4 (0.5)
GENERAL SPECIFICATIONS
Description
Dielectric Strength, Input/Output/Base (50/60Hz)
Minimum Insulation Resistance (@ 500 V DC)
Maximum Capacitance, Input/Output
Ambient Operating Temperature Range
Ambient Storage Temperature Range
Weight (typical)
Housing Material
Terminal Finish
Humidity
RoHS Exemption #’s
Agency Approval
Parameters
3750 Vrms (8)
10
9
Ohm
10 pF
-30 to 80 °C
-40 to 125 °C
1.76 oz (50 g)
UL 94 V0 Self-extinguishing
Sulfamate Nickel
5 - 85% Non condensing
5(a), 7(a), 7(c)-I
UL 508 Listed, E116949
GENERAL NOTES
GENERAL NOTES
1) All parameters at 40°C and per section unless otherwise specified.
2) See derating curves.
3) Off-State dv/dt test method per EIA/NARM standard RS-443, paragraph 13.11.1
4) For UL Listing, must use wire rated @ 75°C
5) For DC output model minimum current spec is 15.7/12.4ma (AC/DC).
6) For DC output model maximum current spec is 27.9/20.3ma (AC/DC).
7) For DC output model, spec is 1K.
8) For DC output model, spec is 2500V
WIRING DIAGRAM
MECHANICAL SPECIFICATIONS
THERMAL DERATE INFORMATION
AGENCY APPROVALS
Designed in accordance with the requirements of IEC 62314
IEC 60068-2-6 : Vibration 0.35mm and 0.75mm Amplitutde over 10-55 Hz
IEC 60068-2-27 : Shock 15G/11ms
IEC 61000-4-2 : Electrostatic Discharge Level 3
IEC 61000-4-4 : Electrically Fast Transients Level 3
IEC 61000-4-5 : Electrical Surges Level 3
E116949
Rev. 100312
LED STATUS FUNCTION TABLE