General Purpose Relays
Power Relays
Potter & Brumfield
T9A Series, DC Coil 30A PCB or Panel Mount Relay
n
n
n
n
n
30A switching in 1 form A (NO) and 20A in 1 form C (CO)
Plastic sealed case available
Meets UL 508 and 873 spacing - 3.18mm through air, 6.36mm over
surface
Option for load connections via 0.250”” (6.35mm) Q.C. terminals
UL class F insulation system standard
Typical applications
HVAC, Appliances, Industrial Controls
Approvals
UL E58304; CSA LR48471
Technical data of approved types on request
Contact Data
Contact arrangement
1 form A (NO), 1 form B (NC), 1 form C (CO)
Rated voltage
277VAC
Max. switching voltage
277VAC
Rated current
30A
15A
20A/10A
Limiting continuous current
30A
Contact material
AgSnOInO, AgCdO
Min. recommended contact load
1A, 5VDC or 12VAC
Initial contact resistance
75 mΩ at 1A at 5VDC or 12VAC
Frequency of operation, with/without load
360/3600hr
Operate/release time max., including bounce
15/15ms
Contact ratings
1)
Type
Load
Factory
AgCdO, 1W coil
NO
30A, 240VAC, general purpose
NO
25A, 240VAC, resistive
CO
20A/10A, 240VAC, general purpose
CO
20A/10A, 240VAC, resistive
CO
20A/10A, 28VDC, resistive
UL 508/873
AgCdO, 1W coil
NO
30A, 240VAC, general purpose
NC
15A, 240VAC, general purpose
CO
20A/10A, 240VAC, general purpose
NC
20A, 240VAC, resistive
CO
16.75A/13.4A, 240VAC, resistive
NO
80LRA/30FLA, 240VAC
NC
30LRA/12FLA, 240VAC
CO
53.6LRA/20FLA / 20LRA/8FLA, 240VAC
NO
98LRA/22FLA, 120VAC
NO
2HP, 240VAC
NC
1/2HP, 240VAC
NO
1HP, 125VAC
NC
1/4HP, 125VAC
NO
10A, 277VAC, ballast
NC
3A, 277VAC, ballast
NO
8.3A, 120VAC, tungsten
NO
5.4A, 277VAC, tungsten
NO
470VA, 120VAC, pilot duty
NO
20A, 28VDC, resistive
NC
10A, 28VDC, resistive
AgCdO - Enhanced Version Only, 1W coil
NO
21A, 250VAC, resistive
NO
25A, 277VAC, resistive
AgCdO, 1W coil (“H” type)
NO
25A, 240VAC, resistive, 105°C
Cycles
100x10
3
100x10
3
100x10
3
100x10
3
100x10
3
100x10
3
100x10
3
100x10
3
6x10
3
6x10
3
30x10
3
30x10
3
30x10
3
100x10
3
1x10
3
1x10
3
1x10
3
1x10
3
6x10
3
6x10
3
6x10
3
6x10
3
30x10
3
100x10
3
100x10
3
250x10
3
100x10
3
6x10
3
Contact ratings
1)
(continued)
Type
Load
UL 508/873
AgSnOInO, 1W coil
NO
30A, 240VAC, general purpose
NO
80LRA/30FLA, 240VAC
NC
10A, 250VAC, resistive
AgCdO, 900mW coil
NO
30A, 240VAC, general purpose
NO
18A, 240VAC, resistive, 105°C
NC
15A, 240VAC, resistive
NO
30LRA/15FLA, 240VAC
NO
50LRA/16FLA, 120VAC
NO
30LRA/11FLA, 120VAC
Cycles
100x10
3
30x10
3
50x10
3
100x10
3
100x10
3
6x10
3
100x10
3
100x10
3
200x10
3
1) Contact ratings at 25°C (unless otherwise noteed) with relay properly vented. Remove
vent nib after soldering and cleaning.
Mechanical endurance
10x10
6
ops.
Coil Data
1) Contact ratings at 25°C (unless otherwise noteed) with relay properly vented. Remove
vent nib after soldering and cleaning.
Coil voltage range
Max. coil power
Max. coil temperature
Coil insulation system according UL
Coil versions, DC coil
Coil
Rated
Operate
code
voltage
voltage
VDC
VDC
Code D (1W) coil
5
5
3.75
6
6
4.5
9
9
6.75
12
12
9
15
15
11.25
18
18
13.5
24
24
18
48
48
36
110
110
82.5
Code L (900mW) coil
5
5
3.75
6
6
4.5
9
9
6.75
12
12
9
15
15
11.25
18
18
13.5
24
24
18
48
48
36
110
110
82.5
5 to 110VDC
110% of nominal
155°C
Class F
Release
voltage
VDC
0.5
0.6
0.9
1.2
1.5
1.8
2.4
4.8
11
0.5
0.6
0.9
1.2
1.5
1.8
2.4
4.8
11
Coil
resistance
Ω±10%
25
36
81
144
225
324
576
2304
12100
27
40
97
155
256
380
660
2560
13450
Rated coil
power
W
1
1
1
1
1
1
1
1
1
.9
.9
.9
.9
.9
.9
.9
.9
.9
All figures are given for coil without preenergization, at ambient temperature +23°C.
09-2015, Rev. 0815
www.te.com
© 2015 Tyco Electronics Corporation,
a TE Connectivity Ltd. company
Datasheets and product specification
according to IEC 61810-1 and to be used
only together with the ‘Definitions’ section.
Datasheets and product data is subject to the
terms of the disclaimer and all chapters of
the ‘Definitions’ section, available at
http://relays.te.com/definitions
Datasheets, product data, ‘Definitions’ sec-
tion, application notes and all specifications
are subject to change.
1
General Purpose Relays
Power Relays
Potter & Brumfield
T9A Series, DC Coil 30A PCB or Panel Mount Relay
(Continued)
Coil Data
(continued)
Insulation Data
Ambient temperature vs. coil voltage – 1W coil
Data below are average values and should be verified in application. Tests
were conducted within a 2’ (.6 m) cube (still air); at nominal coil power @
25°C; with normally open contact loaded; and with 4’ (1.22 m) long, #10
AWG load wires. P.C. board relays were mounted to a 30A, single side P.C.
board. Coil rise test conducted with a 30A PC board to maintain 20°C max.
rize at 30°C. The relay connections and wiring must be designed with an
adequate cross section to ensure proper current flow and heat dissipation.
140
120
Max. Alowable
Ambient Temp. (C)
100
80
60
40
20
0
60
Wash-Tight Relay, Vented
(2
,
Load Connections Via Q.C. Terminals,
PC Mount
Initial dielectric strength
between open contacts
between contact and coil
Initial surge withstand voltage
between contact and coil
Initial insulation resistance
between insulated elements
Clearance/creepage
between contact and coil
1500V
rms
2500V
rms
6kV
1x10
9
Ω
3.18mm clearance/6.3638mm
Other Data
0A
10A
20A
30A
80
100
120
140
Applied Coil Voltage (% of Rated Voltage)
160
180
140
120
100
80
60
40
60
Dust Protected Relay,
Flange Mount
0A
10A
20A
30A
160
180
Material compliance: EU RoHS/ELV, China RoHS, REACH, Halogen content
refer to the Product Compliance Support Center at
www.te.com/customersupport/rohssupportcenter
Ambient temperature
DC coil
-55ºC to 85ºC
3)
105°C models available
Category of environmental protection
IEC 61810
RT0 - open, RTI - dust protected,
RTII - flux proof, RTIII - wash tight
Vibration resistance (functional)
1.65mm max excursions, 10-55 Hz
Shock resistance (functional)
10g for 11msec
Shock resistance (destructive)
100g
Terminal type
pcb-tht and pcb-tht + quick connect
Weight
26g mounting code 1
33g mounting codes 2 and 5
Resistance to soldering heat THT
IEC 60068-2-20
250°C
Packaging/unit
tray/50 pcs., bundle/250 pcs., box/500 pcs.
3) Operating ambient temperature must consider “Must Operate Voltage Change Over
Temperature,” Contact Temperature Rise, Coil Temperature Rise (If coil is not allowed to
cool) and Maximum Coil Temperature. Specification ambient considers 20A load with
coil cooled to ambient.
Max. Alowable
Ambient Temp. (C)
80
100
120
140
Applied Coil Voltage (% of Rated Voltage)
140
120
Max. Alowable
Ambient Temp. (C)
100
80
60
40
20
0
60
Wash-Tight Relay, Vented
(2
PC Terminals For Coil & Contacts
80
100
120
140
Applied Coil Voltage (% of Rated Voltage)
160
0A
10A
20A
30A
180
2) Remove knock-off nib after cleaning process for optimum life of wash-tight relays.
Dimensions
T9AS – Mounting and termination code 2
.250 x .032 QUICK
(6.35 x .81) CONNECT
.130 .020
(3.30 .51)
Ø .03
(.80)
2 PLACES
COM
T9AP – Mounting and termination code 5
.187 x .020
(4.75 x .508)
QUICK
CONNECT
.250 x .032
(6.35 x .81)
QUICK
CONNECT
COM
1.080 MAX.
(27.43)
1.100 MAX.
(27.94)
1.280 MAX.
(32.51)
.045 x .045
(1.14 x 1.14)
.032 x .062
(.81 x 1.57)
1.100 MAX.
(27.94)
1.980 MAX.
(50.29)
1.713 ± .010
(43.51 ± .25)
1.280 MAX.
(32.51)
NO
NC
1.080 MAX.
(27.43)
NC
NO
.071 (1.80) RAD. FOR #6 SCREW
Note:
Recommended mounting screw torque is 4.0-5.0 lbs.in when #6 screw is used.
2
09-2015, Rev. 0815
www.te.com
© 2015 Tyco Electronics Corporation,
a TE Connectivity Ltd. company
Datasheets and product specification
according to IEC 61810-1 and to be used
only together with the ‘Definitions’ section.
Datasheets and product data is subject to the
terms of the disclaimer and all chapters of
the ‘Definitions’ section, available at
http://relays.te.com/definitions
Datasheets, product data, ‘Definitions’ sec-
tion, application notes and all specifications
are subject to change.
General Purpose Relays
Power Relays
Potter & Brumfield
T9A Series, DC Coil 30A PCB or Panel Mount Relay
(Continued)
Dimensions
Plain case
.805 MAX.
(20.4)
.130 + .016
– .010
3.30 + .41
–.25
.212 MAX.
(5.38)
.032 x .062
(.8 x 1.6)
TERMINALS
Bracket mount case
.950 MAX.
(24.13)
(
.69
(17.6)
.50
(12.8)
)
.10 MAX.
(2.54)
.680 MAX.
(17.27)
.130 ± .020
(3.3 ± .51)
.032 x .062
(.8 x 1.6)
TERMINALS
1.280 MAX.
(32.51)
Ø .03
(.80)
TERMINALS
.045 x .045
(1.14 x 1.14)
TERMINAL
1.20 MAX.
(30.5)
.045 x .045
(1.14 x 1.14)
TERMINAL
Ø .03
(0.80)
TERMINALS
1.08 MAX.
(27.43)
.016
(.43)
Terminal assignment
Bottom view on pins
1 Form A
1 Form B
1 Form C
Notes:
1) General tolerance
Diagram Dimensions
<1mm
1~3mm
>3mm
Tolerance
±0.1
±0.2
±0.3
PCB layout
Bottom view on pins
T9AP/S - Mounting and termination code 2
.140 MAX.
(3.56)
.300 .100
(7.62) (2.54)
.600
(15.24) .500
(12.7)
.250 MAX.
(6.35)
.081 ± .005 DIA.
(2.06 ± .13)
.078 ± .003 DIA.
(1.98 ± .08)
.043 ± .003 DIA.
(1.09 ± .08)
2) Dimensions of the pins after tin soldering for PCB type
a) +0.2 for the widht and thickness
b) +0.5 for the lenght
T9AS/V - Mounting and termination code 1
.212 MAX.
(5.38)
.081 ± .005 DIA.
(2.06 ± .13)
.078 ± .003 DIA.
(1.98 ± .08)
.043 ± .003 DIA.
(1.09 ± .08)
Only necessary terminals are
present on single throw models.
Consequently, some holes will
be unnecessary for single throw
models.
.300
(7.62)
.100
(2.54)
.600
(15.24) .500
(12.7)
.150
(3.81)
.550
(13.97)
Only necessary terminals are
present on single throw models.
Consequently, some holes will
be unnecessary for single throw
models.
.150
(3.81)
.550
(13.97)
.700
(17.78)
.700
(17.78)
Product code structure
Type
Typical product code
T9A
S
5
D
2
2
-12
T9A
Power PCB or panel mount relay T9A
Enclosure
N
Open, no enclosure (requires mounting code 1)
P
Dust protected plastic case (requires mounting code 5)
S
Wash-tight plastic case with knock off nib (requires mounting code 1 or 2)
V
Flux-proof plastic case (requires mounting code 1 or 2)
Contact arrangement
1
1 form A (1 NO)
2
1 form B (1 NC)
5
1 form C (1 CO)
Coil Input
D
DC voltage, 1W
L
DC voltage, 900mW
H
1)
DC voltage, 1W (+0/-10 percent coil resistance)
Mounting and termination
1
PCB mounting; PCB terminals for coil and contacts (only available with enclosure code N, S or V)
2
PCB mounting; PCB term. for coil and contacts; 6.35mm (.250in) QC for contacts (only available with enclosure code N, S or V)
5
Flanged mounting; 4.75mm (.187) QC for coil; 6.35mm (.250in) QC for contacts (only available with enclosure code P)
Contact material
2
AgCdO
4
AgSnOInO
7
AgCdO (Enhanced version)
Coil voltage
Coil code: please refer to coil versions table
1)
“H” type coil is only available in mounting termination options 2 & 5.
09-2015, Rev. 0815
www.te.com
© 2015 Tyco Electronics Corporation,
a TE Connectivity Ltd. company
Datasheets and product specification
according to IEC 61810-1 and to be used
only together with the ‘Definitions’ section.
Datasheets and product data is subject to the
terms of the disclaimer and all chapters of
the ‘Definitions’ section, available at
http://relays.te.com/definitions
Datasheets, product data, ‘Definitions’ sec-
tion, application notes and all specifications
are subject to change.
3
General Purpose Relays
Power Relays
Potter & Brumfield
T9A Series, DC Coil 30A PCB or Panel Mount Relay
(Continued)
Product Code
T9AN1L22-24
T9AN5L12-24
T9AN5L22-24
T9AP1D52-12
T9AP1D52-24
T9AP1D52-48
T9AP1D54-24
T9AP5D52-12
T9AP5D52-24
T9AP5D52-48
T9AP5D54-12
T9AP5D54-24
T9AS1D12-5
T9AS1D12-9
T9AS1D12-12
T9AS1D12-15
T9AS1D12-18
T9AS1D12-24
T9AS1D12-48
T9AS1D12-110
T9AS1D14-12
T9AS1D14-24
T9AS1D22-5
T9AS1D22-12
T9AS1D22-24
T9AS1D22-48
T9AS1D22-110
T9AS1L12-12
T9AS1L12-24
T9AS1L22-18
T9AS2L22-24
T9AS5D12-5
T9AS5D12-12
T9AS5D12-18
T9AS5D12-24
T9AS5D12-48
T9AS5D12-110
T9AS5D14-5
T9AS5D22-5
T9AS5D22-12
T9AS5D22-24
T9AS5D22-110
T9AS5D24-5
T9AS5D24-12
T9AS5D24-24
T9AS5L12-12
T9AS5L22-18
T9AS5L22-24
T9AS5L22-48
T9AV1D12-12
T9AV1D12-18
T9AV1D22-18
T9AV1D22-24
T9AV1D22-48
T9AV1L12-12
T9AV1L22-24
T9AV2D22-24
T9AV5D12-24
T9AV5D22-18
T9AV5D22-24
T9AV5L12-12
Enclosure
Open (no cover)
Contacts
1 form A, 1 NO
1 form C, 1 CO
Coil
900mW
Mounting
pcb + QC
pcb terminals
pcb + QC
Flanged mount, QC
Contact Material
AgCdO
Coil
24VDC
Part Number
1419104-6
1-1393210-0
1419104-9
6-1419102-0
6-1419102-3
5-1419102-8
7-1423091-3
5-1419102-4
5-1419102-2
6-1419102-4
7-1423091-4
7-1423091-5
2-1393210-0
2-1393210-2
1-1393210-3
1-1393210-4
1-1393210-5
1-1393210-8
1-1393210-9
1-1393210-2
5-1423091-7
6-1423091-3
2-1419104-3
1-1419104-7
2-1419104-1
2-1419104-2
1-1419104-6
2-1393210-4
2-1393210-5
2-1419104-6
1423794-1
3-1393210-9
3-1393210-3
3-1393210-4
3-1393210-7
3-1393210-8
3-1393210-2
6-1423091-4
3-1419104-9
3-1419104-3
3-1419104-6
3-1419104-2
6-1423091-9
7-1423091-0
7-1423091-1
4-1393210-1
4-1419104-0
4-1419104-1
9-1419136-6
4-1393210-3
5-1393210-2
4-1419148-8
5-1419148-0
2-1423091-3
1-1423091-8
4-1419104-2
1419137-1
4-1393210-8
5-1419148-2
1419137-2
1423091-6
Unsealed, plastic dust cover 1 form A, 1 NO
1W
1 form C, 1 CO
AgSnOInO
AgCdO
AgSnOInO
Wash tight, knock off nib
1 form A, 1 NO
pcb terminals
AgCdO
AgSnOInO
pcb + QC
AgCdO
900mW
pcb terminals
pcb + QC
1 form B, 1 NC
1 form C, 1 CO
1W
pcb terminals
pcb + QC
AgSnOInO
AgCdO
12VDC
24VDC
48VDC
24VDC
12VDC
24VDC
48VDC
12VDC
24VDC
5VDC
9VDC
12VDC
15VDC
18VDC
24VDC
48VDC
110VDC
12VDC
24VDC
5VDC
12VDC
24VDC
48VDC
110VDC
12VDC
24VDC
18VDC
24VDC
5VDC
12VDC
18VDC
24VDC
48VDC
110VDC
5VDC
12VDC
24VDC
110VDC
5VDC
12VDC
24VDC
12VDC
18VDC
24VDC
48VDC
12VDC
18VDC
24VDC
48VDC
12VDC
24VDC
AgSnOInO
900mW
pcb terminals
pcb + QC
AgCdO
Vented, flux tight
1 form A, 1 NO
1W
pcb terminals
pcb + QC
900mW
1 form B, 1NC
1 form C, 1CO
1W
pcb terminals
pcb + QC
pcb terminals
pcb + QC
900mW
pcb terminals
18VDC
24VDC
12VDC
Note. This list represents the most common types and does not show all variants covered by this datasheet. Other types on request.
4
09-2015, Rev. 0815
www.te.com
© 2015 Tyco Electronics Corporation,
a TE Connectivity Ltd. company
Datasheets and product specification
according to IEC 61810-1 and to be used
only together with the ‘Definitions’ section.
Datasheets and product data is subject to the
terms of the disclaimer and all chapters of
the ‘Definitions’ section, available at
http://relays.te.com/definitions
Datasheets, product data, ‘Definitions’ sec-
tion, application notes and all specifications
are subject to change.