Bussmann
®
OPTIMA
™
Overcurrent Protection Module - Fuseholder
for
⁄‹Ω£™∑ ≈ 1⁄Ω™∑
(10mm
≈
38mm) Fuses
OPM-1038
Non-Switch Series
Physical Characteristics:
• Small size matches 45mm IEC starter width.
• Fits #8-18 AWG stranded wire, #10-18 AWG solid wire.
• 3-pole version.
Product Features:
• “Open” fuse indication lights. (Min. 100V required)
• Cam action handle for easy removal.
• Finger safe terminals. (Qualified as IP2O per IEC529)
• Removable module for convenient fuse loading.
• 35mm DIN-rail or screw panel mounting (#8 screw, 1⁄Ω
¢∑
long).
• Dead front construction.
Catalog Symbol:
Series
Fuse Type
Communication
O P M -
1
0 3
8
Blank
- 10 x 38mm
R
- Class CC
C
- Communication
Feature
or 13/32” x 1-1/2”
Additional Features:
• Option for remote “open fuse” status indication feature
available (less down-time).
• Offered with Class CC rejection clips or European 10mm
≈
38mm clips to meet global needs.
• Wire ready: Saves time as terminals are ready to accept
wires.
Materials:
Grey Thermoplastic
UL Flammability:
UL 94VO
Agency Information:
UL - see table below
CSA Certified: C22.2 No. 39, Class 6225-01, File 47235
IEC - see table below
Shipping Weight:
Approx. 213g (.47 lb.)
Carton Quantity:
1
Catalog
Number
OPM-1038
Electrical Rating
30A, 600V UL/CSA**
SC
Rating
*
Clips
Non-rejection,
Remote Open
Fuse Indication
No
UL Information
Std.
File Guide
Recognized
UL 512
E14853
IZLT2
IEC
(Max. 3 Watts per fuse)
32A, 660V IEC
OPM-1038R
30A, 600V UL/CSA**
200kA
10 x 38mm or
13/32” x 1-1/2”
Rejection,
Class CC
Non-rejection,
No
IEC 269-2-1
Listed
UL 512
Recognized
UL 512
Yes
Listed
UL 512
E14853
IZLT
E14853
IZLT2
IEC 269-2-1
E14853
IZLT
OPM-1038C
30A, 600V UL/CSA**
*
Yes
(Max. 3 Watts per fuse)
32A, 660V IEC
OPM-1038RC
30A, 600V UL/CSA**
200kA
10 x 38mm or
13/32” x 1-1/2”
Rejection,
Class CC
*Rating varies depending on fuse used in module.
**DC Voltage Rating: 600V UL/CSA
Recommended Fuse Types:
Class CC
Midget (non-rejection)
LP-CC
KTK
KTK-R
FNM
FNQ-R
FNQ
CE logo denotes compliance with European Union Low Voltage Directive
(50-1000Vac, 75-1500Vdc). Refer to Data Sheet: 8002 or contact
Bussmann Application Engineering at 636-527-1270 for more information.
Applies to OPM-1038 and OPM-1038R.
1-23-04
SB04028
Form No. OPM-1038
Non-Switch Series
Page 1 of 3
Data Sheet: 1102
Bussmann
®
OPTIMA
™
Overcurrent Protection Module - Fuseholder
for
⁄‹Ω£™∑ ≈ 1⁄Ω™∑
(10mm
≈
38mm) Fuses
OPEN FUSE INDICATION
Status Output Specifications:
*Minimum operating voltage: 460Vac, 3-phase
*Maximum operating voltage: 620Vac, 3-phase
Status output maximum conducting current: 40mA
Status output maximum on resistance: 35 ohms
@ 40mA
Status output typical off resistance: >10 Mohm
Status output maximum turn-on and
turn-off delay: 850 milli-second
Status Output Interface Specifications:
Rated Voltage: Recommended 5-35Vdc, 300Vac max.
Rated Current: 40mA max.
Wire Size: #28-14 AWG
Torque: 2.25 lb. in.
Open Fuse Indicator Status Output Description:
The open fuse indicator status output acts very much like
an on/off switch. With all three fuses in place and operating
properly, this status output has a high resistance value of
greater than ten mega-ohms. When one or more of the fuses
are open, the status output becomes turned-on with a
resistance value less than 35 ohms. This status output
withstands voltage (AC or DC) up to 35 volts at off-state
and conducts current up to 40 milli-amps at on-state.
Applying voltage and current exceeding these limits will
result in damage to the components inside this status output
device permanently. There is some time-delay when the
status output changes on/off state. The open fuse
communications or status output device includes optical
isolators within the unit.
Communications output states:
Fuse Good
NO - High Resistance, >10 mega-ohms
Opened Fuse
NC - Low Resistance, < 35 ohms
OPM-1038
Non-Switch Series
The examples shown below illustrate typical interface to
Programmable Logic Controllers.
EXAMPLE 1:
DIRECT INTERFACE TO PC/PLC
PC / PLC
STATUS
OUTPUT
Vcc (5V to 35V)
TTL
Digital
Input
Pull up
Resistor
(> 1K)
EXAMPLE 2:
INTERFACE TO PC / PLC WITH OPTICAL ISOLATION
STATUS
OUTPUT
Optical
Isolator
TTL
Digital
Input
PC / PLC
Vcc (5V to 35V)
Pull up
Resistor
(> 1K)
Current-
Limiting
Resistor
ISOLATED AC OR DC
POWER SOURCE
Note: When energized, a low load terminal voltage will be present when fuses are
open or when pullout module is removed. The leakage current is limited to
.5mA maximum.
Note: Operating this device beyond the above limits will
cause permanent damage to the components on
the board.
For applications requiring status output below a system
voltage of 460V, contact Bussmann.
Example of Output Voltage with three open fuses or pullout module removed.
Catalog Number
OPM-1038, OPM-1038R
OPM-1038C, OPM-1038RC
Type of Indication
Standard
Communication
System Voltage
Load Terminal Voltage
(1L1-3L2-5L3)
(2T1-4T2-6T3)
125Vdc *
12Vdc *
31Vdc *
480Vac, 3-phase
26Vac
56Vac
600Vac, 3-phase
33Vac
88Vac
*The communication device requires a minimum circuit voltage (1L1-3L2-5L3) of
460 volts for the status indicating device to operate. Below 460 volts, but above
120 volts the indicator lights will luminate, but there will not be any communication
status output.
The only controlled copy of this Data Sheet is the electronic read-only version located on the Bussmann Network Drive. All other copies of this document are by definition uncontrolled. This bulletin is
intended to clearly present comprehensive product data and provide technical information that will help the end user with design applications. Bussmann reserves the right, without notice, to change
design or construction of any products and to discontinue or limit distribution of any products. Bussmann also reserves the right to change or update, without notice, any technical information
contained in this bulletin. Once a product has been selected, it should be tested by the user in all possible applications.
1-23-04
SB04028
Form No. OPM-1038
Non-Switch Series
Page 3 of 3
Data Sheet: 1102