UL 489
UL 508
UL 1077
Equipment Breakers
UL 1077
L-Series
AC or DC
UL489 Listed
Circuit Breakers
•
Available in AC and DC models
•
DIN Rail Mounted
•
17.5mm width
•
Thermal Magnetic
•
240V, 480Y/277V AC, 50/60Hz
•
125VDC (1 pole); 250VDC (2 pole)
•
10kA Short Circuit
Interrupting Capacity
•
Positive Trip indicator
(Green - off/tripped, Red - on)
•
HACR Type 40°C
•
Line/Load reversible
Miniature Molded Case
Circuit Breakers
LISTED
E305318
AC Version Current/ Voltage Rating
DC Version Current/ Voltage Rating
Calibration Temperature
Operating Temperature
Storage Temperature
Terminal Size Acceptability
and Torque
0.2-63A/240VAC, 0.2-32A/480Y/277VAC*
0.2-63A/125/250VDC
40°C (104°F)
-25° to 60°C (-13° to 140°F)
-25° to 75°C (-13° to 167°F)
14-3 AWG: 17.5 lb-in. (2.0 Nm)
18-16 AWG: 25 lb-in. (2.8 Nm)
IP20 at front
6,000 cycles on/off
10,000 cycles on/off
copper wire only 60/75°C
3g (18-50Hz)
In any plane
Earth Leakage
Circuit Breakers
Terminal Protection Degree
Electrical Life
Mechanical Life
Wire Connection
Vibration Resistance
Mounting Orientation
*One
device dual voltage ratings.
aC
- short CirCuit interruptinG ratinG
No.
Poles
Type
AC
AC
0.2-32A
10kA@120, 240, 277V
10kA@120, 240V, 480Y/277V
33-63A
10kA@120, 240V
10kA@120, 240V
DC
- short CirCuit interruptinG ratinG
No.
Poles
1
2
Type
DC
DC
0.2-32A
10kA@125V
10kA@250V
33-63A
10kA@125V
10kA@250V
ANNEX
1
2-4
20
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • P 908.806-9400 • F 908.806.9490 • www.altechcorp.com
60
40
Minutes
10
4
1
10
4
Time t
1
0.4
C
10
-1
4x10
-2
Seconds
10
-2
4x10
-3
10
-3
2
3 4
6 8 10 16 20
Multiple of Rated Current
D
Time
versus
Current Trip Curve
For the exact trip curve,
please refer to page 25.
Dimensions in mm
side view
45mm (1.77 in.)
6.5mm
(0.26 in.)
44mm (1.73 in.)
60mm (2.36 in.)
1 PoLe
14.5mm (0.57 in.)
2 PoLe
14.5mm (0.57 in.)
3 PoLe
14.5mm (0.57 in.)
109mm (4.29 in.)
109mm (4.29 in.)
109mm (4.29 in.)
69mm (2.72 in.)
69mm (2.72 in.)
69mm (2.72 in.)
17.5mm (0.69 in.)
17.5mm (0.69 in.)
35mm (1.38 in.)
17.5mm (0.69 in.)
35mm (1.38 in.)
52.5mm (2.07 in.)
Trip-Characteristics*
Characteristic Trip Boundaries
Thermal Trip
Magnetic Trip
Type
Lighting
Wiring
Protection
Control
Circuits
Business
Equipment
Appliances
Applications
Power
Supplies
Heaters
Low
Inrush
High
Inrush
Motors
Reactive
Load
Transformers
Must not Must Trip Must not Must Trip
Trip>100ms
<1hr
Trip>100ms at 100ms
C-Characteristics
1.05xRC
1.05xRC
1.3xRC
1.3xRC
5xRC
5xRC
10xRC
10xRC
AC
DC
D-Characteristics
1.05xRC
1.05xRC
1.3xRC
1.3xRC
10xRC
10xRC
16xRC
16xRC
AC
DC
Warning!
This information should only be used as a selection guide. The use of a Miniature Circuit
Breaker in an application with a certain Trip-Characteristic always requires prototype
testing! It is the responsibility of the circuit design engineer to select the appropriate
Miniature Circuit Breaker for his specific application.
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • P 908.806-9400 • F 908.806.9490 • www.altechcorp.com
21
ANNEX
*The value of each characteristic is shown vertically beneath its corresponding heading.
Earth Leakage
Circuit Breakers
UL 1077
Equipment Breakers
UL 1077
UL 508
UL 489
UL 489
AC
C-Trip
Characteristics
Application Examples:
Low inrush motors, resistive loads, wiring
protection, receptacles, lighting, and
control circuit applications. Relatively
short thermal trip delay and medium
magnetic trip point.
LISTED
E305318
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
12
Weight:
1.7kg (3.74 lb.)
UL 1077
Equipment Breakers
UL 1077
One Pole
Type/
Cat. No.
1CU02L
1CU05L
1CU1L
1CU1.6L
1CU2L
1CU3L
1CU4L
1CU5L
1CU6L
1CU8L
1CU10L
1CU12L
1CU13L
1CU15L
1CU16L
1CU20L
1CU25L
1CU30L
1CU32L
1CU40L
1CU50L
1CU60L
1CU63L
Two Pole
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
6
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
2CU02L
2CU05L
2CU1L
2CU1.6L
2CU2L
2CU3L
2CU4L
2CU5L
2CU6L
2CU8L
2CU10L
2CU12L
2CU13L
2CU15L
2CU16L
2CU20L
2CU25L
2CU30L
2CU32L
2CU40L
2CU50L
2CU60L
2CU63L
UL 508
Three Pole
ANNEX
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
4
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
3CU02L
3CU05L
3CU1L
3CU1.6L
3CU2L
3CU3L
3CU4L
3CU5L
3CU6L
3CU8L
3CU10L
3CU12L
3CU13L
3CU15L
3CU16L
3CU20L
3CU25L
3CU30L
3CU32L
3CU40L
3CU50L
3CU60L
3CU63L
Earth Leakage
Circuit Breakers
Four Pole
Please contact
Altech.
For ring tongue terminal version, replace “U” with “R” in part number. For example
1CR20L
instead of
1CU20L.
22
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • P 908.806-9400 • F 908.806.9490 • www.altechcorp.com
LISTED
E305318
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
12
Weight:
1.7kg (3.74 lb.)
Standard Pack:
6
Weight:
1.7kg (3.74 lb.)
Three Pole
Standard Pack:
4
Weight:
1.7kg (3.74 lb.)
For ring tongue terminal version, replace “U” with “R” in part number. For example
1CR20L
instead of
1CU20L.
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • P 908.806-9400 • F 908.806.9490 • www.altechcorp.com
23
ANNEX
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Type/
Cat. No.
3DU02L
3DU05L
3DU1L
3DU1.6L
3DU2L
3DU3L
3DU4L
3DU5L
3DU6L
3DU8L
3DU10L
3DU12L
3DU13L
3DU15L
3DU16L
3DU20L
3DU25L
3DU30L
3DU32L
3DU40L
3DU50L
3DU60L
3DU63L
Four Pole
Please contact
Altech.
Earth Leakage
Circuit Breakers
UL 1077
Equipment Breakers
UL 1077
One Pole
Type/
Cat. No.
1DU02L
1DU05L
1DU1L
1DU1.6L
1DU2L
1DU3L
1DU4L
1DU5L
1DU6L
1DU8L
1DU10L
1DU12L
1DU13L
1DU15L
1DU16L
1DU20L
1DU25L
1DU30L
1DU32L
1DU40L
1DU50L
1DU60L
1DU63L
Two Pole
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Type/
Cat. No.
2DU02L
2DU05L
2DU1L
2DU1.6L
2DU2L
2DU3L
2DU4L
2DU5L
2DU6L
2DU8L
2DU10L
2DU12L
2DU13L
2DU15L
2DU16L
2DU20L
2DU25L
2DU30L
2DU32L
2DU40L
2DU50L
2DU60L
2DU63L
UL 508
UL 489
AC
D-Trip
Characteristics
Application Examples:
High inrush motors, transformers, power
supplies, heaters and reactive loads.
Relatively long thermal trip delay and very
high magnetic trip point.
UL 489
DC
C- & D-Trip
Characteristics
Application Examples:
Telecommunication equipment,
computer equipment, uninterruptable
power supplies.
LISTED
E305318
C-Trip
UL 508
One Pole
UL 1077
Equipment Breakers
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
12
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
DC1CU02L
DC1CU05L
DC1CU1L
DC1CU1.6L
DC1CU2L
DC1CU3L
DC1CU4L
DC1CU5L
DC1CU6L
DC1CU8L
DC1CU10L
DC1CU12L
DC1CU13L
DC1CU15L
DC1CU16L
DC1CU20L
DC1CU25L
DC1CU30L
DC1CU32L
DC1CU40L
DC1CU50L
DC1CU60L
DC1CU63L
Two Pole
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
6
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
DC2CU02L
DC2CU05L
DC2CU1L
DC2CU1.6L
DC2CU2L
DC2CU3L
DC2CU4L
DC2CU5L
DC2CU6L
DC2CU8L
DC2CU10L
DC2CU12L
DC2CU13L
DC2CU15L
DC2CU16L
DC2CU20L
DC2CU25L
DC2CU30L
DC2CU32L
DC2CU40L
DC2CU50L
DC2CU60L
DC2CU63L
UL 1077
D-Trip
One Pole
ANNEX
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
12
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
DC1DU02L
DC1DU05L
DC1DU1L
DC1DU1.6L
DC1DU2L
DC1DU3L
DC1DU4L
DC1DU5L
DC1DU6L
DC1DU8L
DC1DU10L
DC1DU12L
DC1DU13L
DC1DU15L
DC1DU16L
DC1DU20L
DC1DU25L
DC1DU30L
DC1DU32L
DC1DU40L
DC1DU50L
DC1DU60L
DC1DU63L
Two Pole
Rated
Current
0.2A
0.5A
1.0A
1.6A
2.0A
3.0A
4.0A
5.0A
6.0A
8.0A
10A
12A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Standard Pack:
6
Weight:
1.7kg (3.74 lb.)
Type/
Cat. No.
DC2DU02L
DC2DU05L
DC2DU1L
DC2DU1.6L
DC2DU2L
DC2DU3L
DC2DU4L
DC2DU5L
DC2DU6L
DC2DU8L
DC2DU10L
DC2DU12L
DC2DU13L
DC2DU15L
DC2DU16L
DC2DU20L
DC2DU25L
DC2DU30L
DC2DU32L
DC2DU40L
DC2DU50L
DC2DU60L
DC2DU63L
Earth Leakage
Circuit Breakers
For ring tongue terminal version, replace “U” with “R” in part number. For example
1CR20L
instead of
1CU20L.
24
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • P 908.806-9400 • F 908.806.9490 • www.altechcorp.com