High efficiency: 90.5% @ 3.3V/15A, 48Vin
88.5% @ 3.3V/12A, 24Vin
Size: 33.0x22.8x9.3mm (1.30”x0.90”x0.37”)
Industry standard 1/16th brick size & pinout
Input UVLO
OTP and output OCP, OVP (default is
auto-recovery)
Output voltage trim: -20%, +10%
Monotonic startup into normal and pre-biased
loads
2250V isolation and basic insulation
No minimum load required
SMD and Through-hole versions
ISO 9001, TL 9000, ISO 14001, QS 9000,
OHSAS 18001 certified manufacturing facility
UL/cUL 60950-1 (US & Canada) Recognized
Delphi Series V36SE, 1/16
th
Brick DC/DC
Power Modules: 18~75Vin, 3.3Vo, 50W
The Delphi Series V36SE, 1/16
th
OPTIONS
SMD pins
Positive remote On/Off
Brick, 18~75V wide input, single
output, isolated DC/DC converter, is the latest offering from a world
leader in power systems technology and manufacturing ― Delta
Electronics, Inc. This product family provides up to 50 watts of power
in the industry standard 1/16
th
brick form factor (1.30”x0.90”) and
pinout. With creative design technology and optimization of component
placement, these converters possess outstanding electrical and
thermal performance, as well as extremely high reliability under highly
stressful operating conditions. For the 3.3V output module, it delivers
50W (15A) output with 36 to 75V input and delivers 40W (12A) output
while the input is 18 to 36V to the same module. Typical efficiency of
the 3.3V/15A module is greater than 90.5%. All modules are protected
from abnormal input/output voltage, current, and temperature
conditions. For lower power needs, but in a similar small form factor,
please check out Delta S48SP (36W or 10A) and S36SE (17W or 5A)
series standard DC/DC modules.
APPLICATIONS
Optical Transport
Data Networking
Communications
Servers
DS_V36SE3R315_10252013
TECHNICAL SPECIFICATIONS
(T
A
=25°C, airflow rate=300 LFM, V
in
=48Vdc, nominal Vout unless otherwise noted.)
PARAMETER
ABSOLUTE MAXIMUM RATINGS
Input Voltage
Continuous
Transient (100ms)
Operating Temperature
Storage Temperature
Input/Output Isolation Voltage
INPUT CHARACTERISTICS
Operating Input Voltage
Input Under-Voltage Lockout
Turn-On Voltage Threshold
Turn-Off Voltage Threshold
Lockout Hysteresis Voltage
Maximum Input Current
No-Load Input Current
Off Converter Input Current
2
Inrush Current (I t)
Input Reflected-Ripple Current
Input Voltage Ripple Rejection
OUTPUT CHARACTERISTICS
Output Voltage Set Point
Output Voltage Regulation
Over Load
Over Line
Over Temperature
Total Output Voltage Range
Output Voltage Ripple and Noise
Peak-to-Peak
RMS
Operating Output Current Range
Output Over Current Protection
DYNAMIC CHARACTERISTICS
Output Voltage Current Transient
Positive Step Change in Output Current
Negative Step Change in Output Current
Settling Time (within 1% Vout nominal)
Turn-On Transient
Start-Up Time, From On/Off Control
Start-Up Time, From Input
Maximum Output Capacitance (note1)
EFFICIENCY
100% Load
100% Load
60% Load
ISOLATION CHARACTERISTICS
Input to Output
Isolation Resistance
Isolation Capacitance
FEATURE CHARACTERISTICS
Switching Frequency
ON/OFF Control, Negative Remote On/Off logic
Logic Low (Module On)
Logic High (Module Off)
ON/OFF Control, Positive Remote On/Off logic
Logic Low (Module Off)
Logic High (Module On)
ON/OFF Current (for both remote on/off logic)
Leakage Current (for both remote on/off logic)
Output Voltage Trim Range
Output Voltage Remote Sense Range
Output Over-Voltage Protection
GENERAL SPECIFICATIONS
MTBF
Weight
Over-Temperature Shutdown
NOTES and CONDITIONS
V36SE3R315 (Standard)
Min.
Typ.
Max.
Units
Vdc
Vdc
Vdc
°C
°C
Vdc
Vdc
Vdc
Vdc
Vdc
A
mA
mA
2
As
mA
dB
Vdc
mV
mV
mV
V
mV
mV
A
A
%
0
0
-40
-55
80
100
118
125
2250
48
17
16
1
30
8
1
75
18
17
1.8
3.9
100ms
Refer to figure 19 for measuring point
18
16
15
0.5
100% Load, 18Vin
P-P thru 12µH inductor, 5Hz to 20MHz
120 Hz
Vin=48V, Io=Io.max, Tc=25°C
Io=Io, min to Io, max
Vin=36V to 75V
Tc=-40°C to 85°C
Over sample load, line and temperature
5Hz to 20MHz bandwidth
Full Load, 1µF ceramic, 100µF tantalum
Full Load, 1µF ceramic, 100µF tantalum
Vin = 18V-36V
Vin = 36V-75V
Output Voltage 10% Low
48V, 10µF Tan & 1µF Ceramic load cap, 0.1A/µs
25% Io.max to 50% Io.max
50% Io.max to 25% Io.max
3.267
10
50
3.300
±3
±3
±33
3.30
60
10
0
0
110
12
15
140
3.333
±10
±10
3.40
3.20
100
100
200
30
30
mV
mV
µs
ms
ms
µF
%
%
%
2250
Vdc
MΩ
pF
KHz
0.8
18
0.8
18
1
10
10
140
V
V
V
V
mA
%
%
%
M hours
grams
°C
Full load; 5% overshoot of Vout at startup
Vin = 48V
Vin = 24V
Vin = 48V
90.5
88.5
90.0
10000
10
1000
580
Von/off
Von/off
Von/off
Von/off
Ion/off at Von/off=0.0V
Logic High, Von/off=15V
Pout
≦
max rated power,Io
≦
Io.max
Pout
≦
max rated power,Io
≦
Io.max
Over full temp range; % of nominal Vout
Io=80% of Io, max; Ta=25°C, airflow rate=300FLM
Refer to figure 19 for measuring point
2.4
2.4
-20
115
5.8
12.1
128
Note1: For applications with higher output capacitive load, please contact Delta
V36SE3R315_10252013
2
ELECTRICAL CHARACTERISTICS CURVES
91
88
1
1
POWER DISSIPATION(W)
7
6
5
4
3
2
48Vin
1
0
75Vin
85
82
79
75Vin
76
73
70
10
20
30
40
50
48Vin
24Vin
18Vin
EFFICIENCY(%)
18Vin
24Vin
60
70
80
90
100
10
20
30
40
50
60
70
80
90
100
OUTPUT CURRENT(A%)
OUTPUT CURRENT(A%)
Figure 1:
Efficiency vs. load current for minimum, nominal, and
maximum input voltage at 25°C
18V~36Vin, Io,max is 12A, 36V~75Vin, Io,max is 15A
Figure 2:
Power dissipation vs. load current for minimum,
nominal, and maximum input voltage at 25°C
18V~36Vin, Io,max is 12A, 36V~75Vin, Io,max is 15A
3
2.7
1
INPUT CURRENT (A)
2.4
2.1
1.8
1.5
1.2
0.9
0.6
0.3
0
15
20
25
30
35
40
45
50
55
60
65
70
75
INPUT VOLTAGE (V)
Figure 3:
Typical full load input characteristics at room
temperature
V36SE3R315_10252013
3
ELECTRICAL CHARACTERISTICS CURVES
For Negative Remote On/Off Logic
Figure 4:
Turn-on transient at full rated load current (resistive
load) (10 ms/div). Vin=48V. Top Trace: Vout, 1.0V/div; Bottom
Trace: ON/OFF input, 2V/div
Figure 5:
Turn-on transient at zero load current (10 ms/div).
Vin=48V. Top Trace: Vout: 1.0V/div, Bottom Trace: ON/OFF
input, 2V/div
Figure 6:
Output voltage response to step-change in load
current (50%-25%-50% of Io, max; di/dt = 0.1A/µs; Vin is 24v).
Load cap: 10µF tantalum capacitor and 1µF ceramic capacitor.
Top Trace: Vout (50mV/div, 200us/div), Bottom Trace: Iout
(5A/div). Scope measurement should be made using a BNC
cable (length shorter than 20 inches). Position the load
between 51 mm to 76 mm (2 inches to 3 inches) from the
module.
Figure 7:
Output voltage response to step-change in load
current (50%-25%-50% of Io, max; di/dt = 0.1A/µs; Vin is 48v).
Load cap: 10µF tantalum capacitor and 1µF ceramic capacitor.
Top Trace: Vout (50mV/div, 200us/div), Bottom Trace: Iout
(5A/div). Scope measurement should be made using a BNC
cable (length shorter than 20 inches). Position the load
between 51 mm to 76 mm (2 inches to 3 inches) from the
module.
V36SE3R315_10252013
4
ELECTRICAL CHARACTERISTICS CURVES
Figure 8:
Test set-up diagram showing measurement points for
Input Terminal Ripple Current and Input Reflected Ripple
Current.
Note: Measured input reflected-ripple current with a simulated
source Inductance (L
TEST
) of 12 μH. Capacitor Cs offset
possible battery impedance. Measure current as shown above
Figure 9:
Input Terminal Ripple Current, i
c
, at full rated output
current and nominal input voltage (Vin=48v) with 12µH source
impedance and 33µF electrolytic capacitor (200 mA/div,
1us/div)
Copper
Vo(+)
Strip
10u
Vo(-)
1u
SCO
PE
RESISTIVE
LO
AD
Figure 10:
Input reflected ripple current, i
s
, through a 12µH
source inductor at nominal input voltage (vin=48v) and rated
load current (20 mA/div, 1us/div)
Figure 11:
Output voltage noise and ripple measurement test
setup
3.5
3
OUTPUT VOLTAGE (V)
2.5
2
1.5
1
0.5
0
0
2
4
6
8
10
12
14
16
18
20
LOAD CURRENT (A)
Figure 12:
Output voltage ripple at nominal input voltage
(vin=48v) and rated load current (Io=15A) (50 mV/div,
1us/div).Load capacitance: 1µF ceramic capacitor and 100µF
tantalum capacitor. Bandwidth: 20 MHz. Scope measurements
should be made using a BNC cable (length shorter than 20
inches). Position the load between 51 mm to 76 mm (2 inches
to 3 inches) from the module
Figure 13:
Output voltage vs. load current showing typical
current limit curves and converter shutdown points (Vin=48v)
V36SE3R315_10252013