LED-90W Series– Fixed Output and Dimmable
Switch Mode LED Drivers
Constant Current & Constant Voltage with Isolation
Black Magic Thermal Advantage™ Aluminum Housing
Electrical Specifications
Input Voltage Range:
Input Over-Voltage:
Frequency:
Power Factor:
Inrush Current:
Input Current:
Maximum Power:
Current Accuracy:
Load Regulation:
THD:
Leakage Current:
Hold Up Time:
Protection:
100-277 Vac Nom. (90-305 V Min/Max)
Can endure 320Vac for 48 Hrs, 350Vac for 2 Hrs
50/60 Hz Nom. (47-63 Hz Min/Max)
>0.90 @ full load, 100V through 277V
<30.0 Amps max @ 230 Vac, cold start 25ºC
1.2 Amps max
90W
± 1% Over input line variation
± 3%
< 20% @ full load
_
400 µA Typical
Half Cycle
Output Over-Voltage, Output Over-Current, and
Output Short Circuit Protection reset by power cycling
Electrical Specifications
Minimum Starting Temp:
Maximum Case Temp.
Storage Temperature:
Humidity:
Cooling:
Vibration Frequency:
Sound Rating:
MTBF:
EMC:
-30ºC
90°C
-40ºC to +85ºC
5% to 95%
Convection
5 to 55 Hz/2g, 30 minutes
Class A
418,000 Hours at full load and 40ºC ambient conditions
per MIL-217F Notice 2
FCC 47CFR Part 15 Class B compliant
• Total Power: 90 Watts
• Input Voltage: 100-277 Vac Nom.
• UL Dry & Damp Location Rated
• IP66
• High Power Factor
• UL8750, CSA 22.2, EN61347,
EN61000-3-2, EN61000-3-3 Class C
Constant Current - Product Specifications
Model Number
LED90W-257-C0350-XX
LED90W-200-C0450-XX
LED90W-128-C0700-XX
LED90W-085-C1050-XX
LED90W-064-C1400-XX
LED90W-056-C1600-XX
LED90W-048-C1875-XX
LED90W-036-C2500-XX
LED90W-030-C3000-XX
LED90W-027-C3330-XX
LED90W-025-C3500-XX
LED90W-022-C4090-XX
LED90W-020-C4500-XX
LED90W-018-C5000-XX
LED90W-015-C6000-XX
Output Current Output Voltage
(mA ±3%)
Range
(Vdc)
350
450
700
1050
1400
1600
1875
2500
3000
3330
3500
4090
4500
5000
6000
85-257
66-200
42-128
28-85
21-64
18-56
16-48
12-36
10-30
9-27
8-25
7-22
7-20
6-18
5-15
Max. Output
Power
(W)
90
90
90
90
90
90
90
90
90
90
90
90
90
90
90
Typical
Efficiency
92%
92%
92%
91%
91%
91%
91%
90%
90%
89%
89%
89%
88%
87%
87%
-XX
indicates dimming options are available. See options at left. Blank = fixed current output
Ordering Options:
-D:
0-10V & Resistance dimmable version comes with an extra two wires +Purple/-Gray on
the output side. -D 0-10V Dimming is compatible with most quality 0-10V wall dimmers.
See page 3 for additional specifications.
PWM Dimmable version comes with an extra two wires +Purple/-Gray on the output
side. PD PWM version is PWM Dimmable via a positive 10% to 100% Duty Cycle,
200Hz to 1KHz, 0-10V Pulse. See page 4 for additional specifications.
Constant Voltage - Product Specifications
Model Number
LED90W-015
LED90W-018
LED90W-020
LED90W-022
LED90W-025
LED90W-027
LED90W-030
LED90W-036
Output Voltage Output Current
(Vdc ±5%)
Range
(mA)
15
18
20
22
25
27
30
36
48
56
64
85
128
200
257
1500-6000
1250-5000
1125-4500
1023-4090
875-3500
833-3330
750-3000
625-2500
469-1875
400-1600
350-1400
263-1050
175-700
113-450
88-350
Class 2:
Max. Output
Power
(W)
90
90
90
90
90
90
90
90
90
90
90
90
90
90
90
US/Canada
Typical
Efficiency
87%
87%
88%
89%
89%
89%
90%
90%
91%
91%
91%
91%
92%
92%
92%
US Only
-PD:
Sign Components Manual
E332160
LED90W-048
LED90W-056
LED90W-064
LED90W-085
LED90W-128
Note:
LED drivers are designed and intended to operate LED loads only.
Non-LED loading may be outside the specified design limits of our
LED drivers, and therefore cannot be covered by any warranty.
If you desire to use our LED drivers to operate non-LED loads
please contact us to discuss compatibility.
Specifications subject to change without notice.
LED90W-200
LED90W-257
Rev 8-31-15
Thomas Research Products • 1225 Bowes Rd • Elgin, IL 60123 • T 847-515-3057 • F 847-515-3047 • www.trpssl.com
LED90W Series
SSL Solutions Faster Than The Speed Of Light
®
Pg 2 of 4
Dimensions - Inches (mm)
6.81 [173.0]
2.81 [71.3]
0.16 [4]
0.24 [6]
6.42 [163.0]
7.25 [184.0]
5.91 Min [150 Min]
0.39±0.04 [10±1]
Dimming
Purple (+)
Gray (-)
0.31 [7.8]
WIRE SPECS:
Input Leads:
18 AWG, rated 600 V, 105C, min.
Output Leads:
18 AWG, rated 300 V, 105C, min.
Dimming Leads:
22 AWG, rated 300 V, 105C.
All wires are stranded with solder dipped ends.
0.90 [22.8]
5.91 Min [150 Min]
INPUT
Black (L)
White (N)
Green (GND)
2.24±0.12 [57.0±3]
2.24±0.12 [57.0±3]
OUTPUT
Red (+)
Blue (-)
3.21 [81.5]
Tc = 90°C max
1.00
0.90
0.80
0.70
0.60
Power Factor / Load
50%
45%
40%
35%
THD / Load
0.50
0.40
0.30
0.20
0.10
0.00
50%
60%
70%
120Vac
277Vac
THD
PF
30%
25%
20%
15%
10%
0%
50%
120Vac
277Vac
Load
80%
90%
100%
60%
70%
Load
80%
90%
Lifetime / Case Temperature
350
325
300
275
250
225
200
175
150
125
100
75
50
25
0
45
(Full Load @ 120Vac)
Lifetime
(kHrs)
50
Case Hotspot Temperature
(°C)
55
60
65
70
75
80
85
90
Note:
Life calculations are based on reliability with confidence using
a 90% confidence level and <5% failure rate. At a confidence
level of 90% it is expected that <5% of the parts will fail at
the rated life provided. (Failure is defined as a driver drifting
outside specification, rather than fail to operate)
UL Conditions of Acceptability
See website for additional information
Thomas Research Products • 1225 Bowes Rd • Elgin, IL 60123 • T 847-515-3057 • F 847-515-3047 • www.trpssl.com
1.83 [46.5]
100%
0.39±0.04 [10±1]
1.06 [27]
LED90W Series
SSL Solutions Faster Than The Speed Of Light
®
Pg 3 of 4
“-D” Option: 0-10VDC and Resistance Dimming
Parameters
Source Current out of 0-10V Purple Wire
Absolute Voltage Range on 0-10V (+) Purple Wire
Minimum
0 mA
-2.0 V
Typical
—
—
Maximum
2 mA
+15 V
Typical Dimming Circuit
Dim (+) Purple
LED90W-xxx-Cxxxx-D
IP710 Wall Dimmer
Dim (-) Gray
(Dimmer must be current-sink type control)
100
90
80
70
60
50
40
30
20
10
0
Output Current / 0-10VDC Dimming Input
Output Current %
0V
1V
2V
3V
Dimming Input
(Vdc)
4V
5V
6V
7V
8V
9V
10V
Notes:
1.
2.
3.
4.
0-10V dimmable version comes with an extra two wires +Purple/-Gray on the output side.
Compatible with most 0-10V Wall Slide dimmers and direct 0-10V analog signal. Recommended dimmer is Leviton IP710 or equivalent
0-10V dimmable version is not intended to dim below about 5% @ 0V or 10% @ 1.0V
0-10V dimmable version output will be 100% with Purple/Gray open and minimum with Purple/Gray Shorted.
Thomas Research Products • 1225 Bowes Rd • Elgin, IL 60123 • T 847-515-3057 • F 847-515-3047 • www.trpssl.com
LED90W Series
SSL Solutions Faster Than The Speed Of Light
®
Pg 4 of 4
“-PD” Option: PWM Dimming
Parameters
Absolute Maximum Voltage Range on PWM Input (Purple Wire)
Input LOW Level Voltage Range (Purple Wire)
Input HIGH Level Voltage Range (Purple Wire)
Sink Current into PWM Input (Purple Wire)
PWM Input Signal Frequency
PWM Input Signal Positive Duty Cycle
Minimum
-2.0V
-2.0
+9.0
0mA
200Hz
0%
Typical
10V
0V
10V
—
—
10-90%
Maximum
+28V
+7.5V
28V
1.2mA
1000Hz
100%
PWM Positive Dimming Typical Circuit
PWM (+) Purple
LED90W-xxx-Cxxxx-PD
PWM In
PWM (-) Gray
100
90
80
70
60
50
40
30
20
10
0
Output Current / Positive Duty Cycle
Output Current %
0%
10%
20%
30%
Positive Duty Cycle
40%
50%
60%
70%
80%
90%
100%
Notes:
1. PWM Dimmable version comes with an extra 2 wires +Purple/-Gray on the output side.
2. Below 10% Duty cycle proper dimming operation is not assured. Unit is not intended to turn off at <10% Duty Cycle.
3. PWM dimmable version output will be 100% with Purple/Gray open and minimum with Purple/Gray Shorted.
Thomas Research Products • 1225 Bowes Rd • Elgin, IL 60123 • T 847-515-3057 • F 847-515-3047 • www.trpssl.com