CE marked for all applicable directives, UL and C-UL.
TUV certified: CM-S1, CM-S2, CM-S3, CM-S11 and CM-S31.
Specifications are subject to change without notice.
Note: The safety contacts of the STI switches are described as normally closed (N/C) i.e., with the guard closed, actuator in place, and
the machine able to be started.
Humidity:
Compliance
Standards:
Approvals/Listings:
95% RH at 55°C (131°F)
2
www.omron247.com
CM Series
Safety Interlock Switches
Control Unit Specifications
Electrical
Power Supply:
Power Consumption:
Input Fuse:
Safety Inputs:
CM-S4
24 VAC/DC ± 10%
2.4 VA typical, 0.25 A quick acting
500 mA resetable
1 N/O + 1 N/C
CM-S30
24 VAC/DC ± 10%
120 mA
750 mA resetable
1 N/O + 1 N/C
CM-S41, CM-S21 & CM-SE
CM-S41 — 24 VAC/DC, 110/230 VAC
CM-S21 & CM-SE — 24 VAC/DC
CM-S41 — 6 VA;
CM-S21 & CM-SE — 3 VA
500 mA resetable
CM-S41 —
4 CM-S11 or CM-S31 switches
CM-S21 —
2 CM-S11 or CM-S31 switches
CM-SE — 5 CM-S11 or CM-S31 switches
100 m (328 ft.)
Contact factory
CM-S41 & CM-S21 — 2 N/O;
CM-SE — N/A
4 A / 230 VAC; 2 A / 24 VDC (resistive)
10 V / 10 mA
250 V
Deactivation by sensor 13 mS
AC = 5 A; DC = 2.5 A; quick acting
Monitored manual or automatic
N/C loop between X1 and X2
35 mm (1.38 in.) DIN rail
Polycarbonate
1 x 2.5 mm
2
stranded, 1 x 4 mm
2
solid
CM-S41 — 575 g (20.3 oz.)
CM-S21 — 183 g (6.5 oz.)
CM-SE — 135 g (4.8 oz.)
Red
Power = Red
Outputs Closed: Green = On
Outputs Open: No Light = Off
Gate Closed: Yellow = On
Gate Open: No Light = Off
1 x 10
6
Housing IP40, Terminals IP20
10 to 55°C (50 to 131°F)
85%
Max Cable Length:
Max Input Resistance:
Relay Outputs:
Max Switched Current/Voltage:
Min Switched Current/Voltage:
Impulse Withstand Voltage:
Max Drop-Out Time:
Max Output Fuse:
Reset Mode:
External Device Monitoring:
Mechanical
Mounting:
Case Material:
Max Wire Size:
Weight:
—
Contact factory
1 N/O safety + 1 N/O aux.
4 A / 24 VAC/DC
4 mA / 12 V
250 V
18 ms
4 A quick acting
Automatic
N/C loop between Y1 and Y2
35 mm (1.38 in.) DIN rail
Polyamid PA6.6
2 x 2.5 mm
2
(12 AWG)
240 g (8.5 oz.)
—
Contact factory
2 N/O safety + 1 N/C aux.
3 A / 24 VAC/DC
4 mA / 12 V
250 V
18 ms
4 A quick acting
Automatic/Manual, monitored
Between Y1, Y2, Y3
35 mm (1.38 in.) DIN rail
Polyamid PA6.6
1 x 2.5 mm
2
(14 AWG)
230 g (8.1 oz.)
Color:
Indication:
EN292, EN60204-1, EN954-1,EN1088,
EN60947-5-3, EN947-5-3, EN50081,
EN50082, EN61000-6-2
Approvals/Listings:
CE marked for all applicable directives, UL and C-UL, TUV (TUV pending for CM-S30)
Safety Category:
Cat 3 per EN954-1
Cat 4 per ISO 13894-1
Cat 3 per EN954-1
(internal operation)
(internal operation)
(internal operation)
Specifications are subject to change without notice.
Note: The safety contacts of the STI switches are described as normally closed (N/C) i.e., with the guard closed, actuator in place, and the machine able to
be started.
Mechanical Life:
Environmental
Protection:
Operating Temperature:
Humidity:
Compliance
Standards:
Grey
U: Green = On
Outputs Open: Red = On
Outputs Closed: Green = On
D11, D12, D21, D22: Green = Gate closed
D31, D32, D41, D42: Red = Gate open
3 x 10
7
Housing IP40, Terminals IP20
0 to 50°C (32 to 122°F)
95%
Red/Grey
Green = Power On
Green = K1 On
Green = K2 On
1 x 10
7
Housing IP40, Terminals IP20
0 to 55°C (32 to 131°F)
93%
EN292, EN60204-1, ISO 13849-1, EN1088, EN60947-5-3, EN947-5-3,
EN50081, EN50082, EN61000-6-2
www.omron247.com
3
CM Series
Safety Interlock Switches
Applications
2-Wire Single Channel Controllers
CM-S41 Control Unit
The CM-S41 is a combined Safety Switch and E-Stop control
unit. Along with the ability to monitor up to four, 2-wire CM Series
safety switches, it can also monitor the normally closed contacts
of emergency stop buttons or mechanical safety switches in dual
channel control circuits.
The CM-S41 has 2 normally open safety contact outputs and 1
normally closed auxiliary output, an external reset/proving circuit
and LED indication for “Power”, “Run” and the status of each
activated gate switch.
CM-S21 Control Unit
The CM-S21 control unit is a 24 VAC/DC system that can moni-
tor up to 2 CM Series safety switches.
The CM-S21 has 2 normally open safety contact outputs and 1
normally closed auxiliary output, an external reset/proving circuit
and LED indication for “Power”, “Run” and the status of each
activated gate switch.
CM-SE Extender Module
The CM-SE expansion module is a 24 VAC/DC unit that can be
added to either the CM-S41 or CM-S21 to monitor an additional
5 CM Series safety switches. Connection to the main control
unit is by a simple 2-wire bus connection. The status of each
guard switch is shown by the YELLOW LED’s. Additional CMS-E
modules can be added to monitor larger systems.
CM-S21 Application Diagram
24V
(+ve)
GS1
A1 X1 BL DR 31 13 23
GATE 1
POWER
IND 1
IND 2
RUN
K1
K2
MANUAL
RE-SET
GATE 2
A2 X2 BL DR 32 14 24
F1
GS2
0V
(-ve)
K1
K2
K1
K2
CM-S41 Application Diagram
CM-SE Application Diagram
L (+ve)
GS1 GS2
24 V
+ve
Extender Module
GS1 GS2 GS3
F2
Control Unit
MECHANICAL
SAFETY
SWITCHES
or
EMERGENCY
STOP
A1 S13 S23 X1 BL DR BL DR 31 13 23
GATE 1 GATE 2
K1
K2
A1 DR BL DR BL DR BL
GATE 1 GATE 2 GATE 3
POWER
IND 1
IND 2
IND 3
IND 4
A1
POWER
1
RUN
2
DE-SELECT
GATE 2
GATE 3
GATE 4
3
4
MANUAL
RE-SET
GATE 4 GATE 5
IND 5
ISIS-4 or ISIS-2
CM-S41 / CM-S21 Control
CONTROL UNIT
Units:
Connect the CM-SE Bus
Connect the ISIS-E
connection to an active
to
Bus connection
gate input.
A2
BL DR
BUS
GATE 3 GATE 4
A2 S14 S24 X2 BL DR BL DR 32 14 24
A2 DR BL DR BL DR BL
F1
F2
GS4 GS5
K1
K2
GS3 GS4
K1
N (-ve)
K2
0V
-ve
2-WIRE BUS CONNECTION
4
www.omron247.com
CM Series
Safety Interlock Switches
Applications (continued)
Dual Channel Controllers
CM-S4 Control Unit
The CM-S4 controller is capable of monitoring up to four,
magnetically coded switches with 1 N/O + 1 N/C contacts up to
category 3 according to EN954-1. The CM-S4 has a dedicated
dual channel input for each switch and has LED status indicators
for each channel. The CM-S4 has 1 N/O safety contact and 1 N/O
Aux contact. External Device Monitoring (EDM) is available using
Y1,Y2 inputs.
CM-S30 Control Unit
The CM-S30 controller is capable of monitoring one magneti-
cally coded switch with 1 N/O + 1 N/C contacts up to category
4, or two switches to category 3 according to ISO 13489-1. The
CM-S30 control unit is capable of monitoring up to 30 convention-
al read style switches in series, but does not conform to category
4 when used with more than two switches. The CM-S30 controller
has 2 N/O safety contacts and 1 N/C Auxiliary contact. External
Device Monitoring (EDM) is available using Y1,Y2 inputs.
Question to the moderator:1. All three SPI interfaces need to be connected to 5V peripherals (a total of 12 AD9835s). SPI1 and SPI2 can be set to open drain and pulled up to 5V externally with resisto...
I want to write through the serial port. When I input more than 9 chars in the serial port debugging assistant and click send, the return value of aci_gatt_write_without_resp is only 9 successful, and...
Hello everyone, I want to spend a lot of time to learn computer hardware knowledge as comprehensively as possible. What books should I read? I plan to concentrate on learning computer hardware technol...
[i=s]This post was last edited by paulhyde on 2014-9-15 03:48[/i] Power supply... DCDC module, four days and three nights, sleeping value is less than 10*3600 seconds. Finally it was called out, but t...
The topic I applied for at the beginning was to make a sous vide device. You can search Baidu or Google for information about sous vide. The general idea is low-temperature cooking, using a constant t...