Self Powered AC Current Transducer
DIN RAIL / PANEL MOUNT, AVERAGE RMS
The
CR4210
and
CR4211
Series Current Transducers
are self powered. These transducers are calibrated to
provide a 0-5 VDC and 0-10 VDC signal that is
proportional to the average RMS input AC current.
Designed for multi-point current sensing, these devices
provide excellent features in a high value package.
Applications
Multi-point current sensing and control panels
Remote current sensing
Monitor motor faults
Monitor heating elements
Monitor lighting elements
CR4210 CR4211
C
Transducers
Single Element - .79” Window
2 to 200 AAC Input Range
Features
35mm DIN Rail or Panel Mount
Available with 0 - 5 VDC or 0-10 VDC outputs
Self powered, requires no external power source
Use with external current transformers
Low cost
Connection diagram printed on case
Regulatory Agencies
Recognized to UL 61010B-1
Recognized to CAN/CSA-C22.2, No. 61010-1-2004
Meets requirement of IEC 61010-1 and BS EN 61010-1
CR4210S CR4211S
Single Element - 1.22” Window
2 to 200 AAC Input Range
E199795
All single phase current transducers are
available in split core design. Simply put
an “S” at the end of the prefix*
I.E. CR4210S-10
* Not UL Recognized
Average 3 Phase Sensing
Add suffix for input range
2
5
10
20
50
70
100
150
200
-
-
-
-
-
-
-
-
-
0-2 AAC
0-5 AAC
0-10 AAC
0-20 AAC
0-50 AAC
0-70 AAC
0-100 AAC
0-150 AAC
0-200 AAC
PART NUMBERS
CR4210(S)
CR4211(S)
Single element with 0 - 5 VDC output (split core design)
Single element with 0 - 10 VDC output (split core design)
*
*
CR4210S and CR4211S only available in ranges 20 amps and above
-
-
Ranges available up to and including
600 AAC
The Professional
Energy Monitoring
Company
ISO 9001:2008 Quality Management System
M N TI
3500 Scarlet Oak Blvd. St. Louis MO USA 63122 V: 636-343-8518 F: 636-343-5119
Web: http://www.crmagnetics.com
34
E-mail: sales@crmagnetics.com
Self Powered AC Current Transducer
DIN RAIL / PANEL MOUNT, AVERAGE RMS
SPECIFICATIONS
Basic Accuracy:.............................. 0.5%
Linearity:......................................... 10% to 100% FS
Thermal Drift:.................................. 500 PPM/°C
Operating T
emperature:.................
Installation Category:....................
Cleaning:........................
Output Load:..................
1M
Water-dampened cloth
Ω
or Greater
Vibration T
ested T
o:........................IEC 60068-2-6,1995
Pollution Degree:...........................
Insulation Voltage:........................
2
CAT II
0°C to +60°C
Response Time:.............
Relative Humidity:..........
31°C
80% for temperatures up to
250 ms max., 0-90%FS
Altitude:.........................................
Frequency Range:.........................
Calibration:..............Average Sensing, RMS Calibrated
50Hz - 400Hz
2000 meter max.
2500 VDC
Supply Power:................
obtained from current-sensing
conductor)
Self powered (output voltage is
50% at 40°C
and decreasing linearly to
T
orque Specs.:................
MTBF:....................................Greater than 100 K Hours
Weight:............................
3.0 inch lbs. (0.4Nm)
0.5 lbs.
OUTLINE DRAWING
(36)
0.14
(3.5)
9
8
7
6
5
1
2
3
4
C
Transducers
1.06
(26.8)
2.874
(73)
2.874
(73)
0.79 1.22 Split core
(20) (31) DIA.
0.79 1.22
2.99 3.86 Split core
(76) (98)
0.20
(5.1)
1.42
3.268
(83)
(36)
1 hole: 0.79(20) Dia. for CR4210 & 4211 (shown)
CONNECTION DIAGRAM
1
Request CR Magnetics Low & Medium Voltage
Current Transformers Catalog.
2
3
4
9
8
7
6
5
+
OUTPUT 1
-
CR4210
Single Element 0 - 5 VDC Output
CR4211
Single Element 0 - 10 VDC Output
NOTE: The building installation must have a switch or circuit-breaker that is in close proximity and within easy reach of the operator. The switch or circuit breaker
shall be marked as the disconnecting device for the equipment.
The Professional
Energy Monitoring
Company
ISO 9001:2008 Quality Management System
M N TI
3500 Scarlet Oak Blvd. St. Louis MO USA 63122 V: 636-343-8518 F: 636-343-5119
Web: http://www.crmagnetics.com
35
E-mail: sales@crmagnetics.com