TECHNICAL DATASHEET
PMC Panel Mount Power Supply
24V 100W 1 Phase / PMC-24V100W1A
□
PMC
Highlights & Features
–
–
–
–
–
–
Universal AC input range
Power will not de-rate for the entire input voltage range
Full corrosion resistant aluminium casing
High MTBF > 700,000 hrs. as per Telcordia SR-332
Safety approval according to IEC/EN/UL 60950-1
Also available: IP20 and Front Face connectors
Safety Standards
CB Certified for worldwide use
Model Number:
PMC-24V100W1A☐
Unit Weight:
0.41 kg (0.90 lb)
Dimensions (L x W x D):
158 x 97 x 38 mm
(6.22 x 3.82 x 1.5 inch)
General Description
The new Panel Mount Power Supply is the latest offering from one of the world’s largest power supply manufacturers and solution
providers - Delta. The product range offers a nominal output voltage of 24V, a wide temperature range from -10°C to +70°C and a
highly dependable minimum holdup time. The state-of-the-art design is made to withstand harsh industrial environments. What makes
the product stands out from the crowd is its lightweight full aluminum body design which can withstand shock and vibration according to
IEC 60068-2-6. Delta’s Panel Mount Power Supply also offers overvoltage and overload protection. Using a wide input voltage range
design, it is compatible worldwide. The input also includes DC operating voltage from 125-375Vdc. Best of all, this excellent design and
quality does not come with a big price tag.
Model Information
PMC Panel Mount Power Supply
Model Number
PMC-24V100W1A☐
Input Voltage Range
85-264Vac (125-375Vdc)
Rated Output Voltage
24Vdc
Rated Output Current
4.17A
Model Numbering
PM
Panel Mount
C–
Product Type
C – Enclosed
24V
Output Voltage
100W
Output Power
1
Single Phase
A
No PFC
□
Connector Type
A – Terminal Block
J – IP20 Terminal Block*
L – Front Face*
*Options
1
All parameters are specified at 25°C ambient and AC input unless otherwise indicated.
www.DeltaPSU.com (March 2016, Rev. 01)
TECHNICAL DATASHEET
PMC Panel Mount Power Supply
24V 100W 1 Phase / PMC-24V100W1A
□
Specifications
Input Ratings / Characteristics
Nominal Input Voltage
Input Voltage Range
Nominal Input Frequency
Input Frequency Range
Nominal DC Input Voltage*
DC Input Voltage Range*
Input Current
Efficiency at 100% Load
Max Inrush Current (Cold Start)
Leakage Current
* Safety approval according to IEC/EN/UL 60950-1.
100-240Vac
85-264Vac
50-60Hz
47-63Hz
125-250Vdc
125-375Vdc
< 2.0A @ 115Vac, < 1.1A @ 230Vac
> 86% @ 115Vac & 230Vac
< 50A @ 115Vac, < 100A @ 230Vac
< 1mA @ 240Vac
Output Ratings / Characteristics**
Nominal Output Voltage
Factory Set Point Tolerance
Output Voltage Adjustment Range
Output Current
Output Power
Line Regulation
Load Regulation
PARD*** (20MHz)
Rise Time
Start-up Time
Hold-up Time
Dynamic Response (Overshoot & Undershoot O/P Voltage)
Start-up with Capacitive Loads
**For power de-rating from 50°C to 70°C, see power de-rating on page 3.
***PARD is measured with an AC coupling mode, 5cm wires, and in parallel with 0.1µF ceramic capacitor & 47µF electrolytic capacitor
.
24Vdc
24Vdc ± 2%
22-28Vdc
4.17A (100W max.)
100W
< 0.5% typ. (@ 85-264Vac input, 100% load)
< 1% typ. (@ 85-264Vac input, 0-100% load)
< 150mVpp
< 30ms @ nominal input (100% load)
< 1000ms @ nominal input (100% load)
> 15ms @ 115Vac, > 90ms @ 230Vac (100% load)
± 5% @ 85-264Vac input, 0-100% load
(Slew Rate: 0.1A/μS, 50% duty cycle @ 5Hz to 100Hz)
8,000µF Max
2
All parameters are specified at 25°C ambient and AC input unless otherwise indicated.
www.DeltaPSU.com (March 2016, Rev. 01)
TECHNICAL DATASHEET
PMC Panel Mount Power Supply
24V 100W 1 Phase / PMC-24V100W1A
□
Mechanical
Case Chassis / Cover
Dimensions (L x W x D)
Unit Weight
Indicator
Cooling System
Terminal
PMC-24V100W1AA
PMC-24V100W1AJ
PMC-24V100W1AL
Wire
Noise (1 Meter from power supply)
Aluminium
158 x 97 x 38 mm (6.22 x 3.82 x 1.5 inch)
0.41 kg (0.90 lb)
Green LED (DC OK)
Convection
M3.5 x 7 Pins (Rated 300V/15A)
M3.5 x 7 Pins (Rated 300V/20A)
M3.5 x 7 Pins (Rated 300V/20A)
Refer to page 7
Sound Pressure Level (SPL) < 40dBA
Environment
Surrounding Air Temperature
Power De-rating
Operating Humidity
Operating Altitude
Shock Test (Non-Operating)
Vibration (Non-Operating)
Pollution Degree
Operating
Storage
-10°C to +70°C
-25°C to +85°C
> 50°C de-rate power by 2.5% / °C
5 to 95% RH (Non-Condensing)
3,000 Meters (9,840 ft.)
IEC 60068-2-27, 30G (300m/S²) for a duration of 18ms,
3 times per direction, 18 times in total
IEC 60068-2-6, 10Hz to 150Hz @ 50m/S² (5G peak);
90 min per axis for all X, Y, Z direction
2
Protections
Overvoltage
Overload / Overcurrent
Over Temperature
Short Circuit
Degree of Protection
Protection Against Shock
*PE: Primary Earth
< 32V ±10%, SELV Output, Hiccup Mode,
Non-Latching (Auto-Recovery)
> 120% of rated load current, Hiccup Mode,
Non-Latching (Auto recovery)
< 75°C Surrounding Air Temperature @ 100% load,
Non-Latching (Auto-recovery).
Hiccup Mode, Non-Latching
(Auto-recovery when the fault is removed).
IP20 (PMC-24V100W1AJ)
Class I with PE* connection
Reliability Data
MTBF
Expected Cap Life Time
> 700,000 hrs, as per per Telcordia SR-332
I/P: 115Vac, O/P: 100% load, Ta: 25°C
10 years (115Vac & 230Vac, 50% load @ 40°C)
3
All parameters are specified at 25°C ambient and AC input unless otherwise indicated.
www.DeltaPSU.com (March 2016, Rev. 01)
TECHNICAL DATASHEET
PMC Panel Mount Power Supply
24V 100W 1 Phase / PMC-24V100W1A
□
Safety Standards / Directives
Electrical Safety
Nemko Bauart
UL/cUL recognized
CCC
CB scheme
CE
Material and Parts
Galvanic Isolation
Input to Output
Input to Ground
Output to Ground
EN 60950-1
UL 60950-1 and CSA C22.2 No. 60950-1
(File No. E191395)
GB4943.1
IEC 60950-1
In conformance with EMC Directive 2004/108/EC and
Low Voltage Directive 2006/95/EC
RoHS Directive 2011/65/EU Compliant
3.0KVac
1.5KVac
0.5KVac
EMC
EMC / Emissions
Immunity to
Electrostatic Discharge
IEC 61000-4-2
CISPR 22, EN 55022, FCC Title 47: Class B, GB9254.1
Generic Standard: EN 55024
Level 4 Criteria A
1)
Air Discharge: 15kV
Contact Discharge: 8kV
Level 3 Criteria A
1)
80MHz-1GHz, 10V/M with 1kHz tone / 80% modulation
Level 3 Criteria A
1)
2kV
Level 3 Criteria A
1)
2)
Common Mode : 2kV
3)
Differential Mode : 2kV
Level 3 Criteria A
150kHz-80MHz, 10Vrms
Criteria A
1)
10A/Meter
100% dip; 1 cycle (20ms); Self Recoverable
Level 3 Criteria A
1)
2)
Common Mode : 2kV
3)
Differential Mode : 1kV
IEC/EN 61000-3-2, Class A; GB17625.1
IEC/EN 61000-3-3
1)
Radiated Field
Electrical Fast Transient / Burst
Surge
IEC 61000-4-3
IEC 61000-4-4
IEC 61000-4-5
Conducted
Power Frequency Magnetic Fields
Voltage Dips
Low Energy Pulse Test (Ring Wave)
IEC 61000-4-6
IEC 61000-4-8
IEC 61000-4-11
IEC 61000-4-12
Harmonic Current Emission
Voltage Fluctuation and Flicker
1) Criteria A: Normal performance within the specification limits
2) Asymmetrical: Common mode (Line to earth)
3) Symmetrical: Differential mode (Line to line)
4
All parameters are specified at 25°C ambient and AC input unless otherwise indicated.
www.DeltaPSU.com (March 2016, Rev. 01)
TECHNICAL DATASHEET
PMC Panel Mount Power Supply
24V 100W 1 Phase / PMC-24V100W1A
□
Block Diagram
Device Description
PMC-24V100W1AA:
Terminal Block
PMC-24V100W1AJ:
IP20 Terminal
PMC-24V100W1AL:
Front Face
1)
2)
3)
Input & Output terminal block connector
DC voltage adjustment potentiometer
DC OK control LED (Green)
All parameters are specified at 25°C ambient and AC input unless otherwise indicated.
www.DeltaPSU.com (March 2016, Rev. 01)
5