PSB-360 Series
Specifications
Features:
(2 Phase)
• Multiple overload/ short circuit protection modes
• Efficiency above 91%
• Easy parallel connection for more power
• Small size
• DIN rail mountable
• Cooling by free air convection
• UL508 (industrial control equipment) approved
• EN60950-1
• Built-in DC OK relay contact
• 3 year warranty
OUTPUT
Cat. No.
DC VOLTAGE
RATED CURRENT
CURRENT RANGE
RATED POWER
RIPPLE & NOISE (max)
VOLTAGE ADJ. RANGE
VOLTAGE TOLERANCE
START UP WITH STRONG LOAD
CURRENT SHORT CIRCUIT Icc
PSB-36024
24 V
14 A
Refer to Output derating curve
336 W
100 mVp-p
Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1µF & 47µF parallel capacitor.
DISSIPATION POWER LOAD mas
LINE REGULATION
LOAD REGULATION
SETUP, RISE TIME
22 V ~ 27 V
-0.03
Tolerance: includes set up tolerance, line regulation and load regulation.
≤
50,000 µF
30 A
Max 2 sec.: Hiccup mode
Permanent: Continuous mode
28 W
± 0.5%
± 1%
1 sec. (max)
Length of set up time is measured at cold first start. Turning ON/OFF the power supply may lead to increase of the set up time.
INPUT
HOLD UP TIME (Typ.)
VOLTAGE RANGE
FREQUENCY RANGE
EFFICIENCY (Typ.)
AC CURRENT (230 – 400 – 500 Vac.)
INRUSH CURRENT (Typ.)
INTERNAL FUSE
EXTERNAL FUSE (recommended)
LEAKAGE CURRENT
OVERLOAD
OVER VOLTAGE
OVER TEMPERATURE
SHORT CIRCUIT PROTECTION
DC OK AKTIV SIGNAL (max.)
WORKING TEMP.
HUMIDITY
STORAGE TEMP
TEMP. COEFFICIENT
VIBRATION
SAFETY STANDARDS
WITHSTAND VOLTAGE
PROTECTION CLASS
ISOLATION RESISTANCE
EMI CONDUCTION & RADIATION
HARMONIC CURRENT
EMS IMMUNITY
Typ. 20 msec
187 ~ 264 V AC / 330 ~ 550V AC by switch
47 ~ 63 Hz +-6%
>91 %
2.2 ~ 1.4 ~ 1.0 A
< 17 A < 5 msec
T4A
16 A (MCB curve B)
< 1.5 mA @ 500 Vac
In (60°C) x 1.5 ³ 3 min.;
Current max. Overload @ 4Vdc (permanent) Imax=In (60°C) x (1.8 ~ 2.2)
30 ~ 35 Vdc
Yes. Shuts down output and automatically restarts when the temperature inside goes down
1 Hiccup Mode / 2 Fold Back / 3 Restart After Main - Selectable
20 ~ 30 Vdc
-25 up to +70 °C
(>60°derating 2.5% °C)
95 % at 25°C, no condensation
-40 up to +85 °C
± 0.03% / C° (0 ~ 60 °C)
In according to IEC60068-2-6
UL508 approved, IEC/EN 60950, EN 50178, IEC/EN 60950, EN60950-1, PELV EN 60204-1
I/P-O/P: 3k VAC I/P-FG: 1.6k VAC
O/P-FG: 500 VAC
IP 20 (EN/IEC 60529)
100 MΩ (min) @ 500 Vdc
EN61000-6-4
EN61000-3-2
EN 61000-4-2, EN 61000-4-3, EN 61000-4-4, EN 61000-4-5,
EN 61000-4-6, EN61000-6-2, EN61000-6-4,
The power supply is considered a component which will be installed into a final equipment. The final equipment must be
re-confirmed that it still meets EMC directives.
PROTECTION
ENVIRONMENT
SAFETY & EMC
OTHERS
MTBF IEC 61709
POLLUTION DEGREE
CONNECTION TERMINAL BLOCK
DIMENSION
PACKING
NOTE
> 500.000 h
2
2.5 mm Screw (24 ~ 14 AWG)
72x115x135 mm ( 2.8x4.5x5.3 in )
0.65 kg (1.3 lbs) each
All parameters NOT specially mentioned are measured at 230V AC input, rated load and 25˚C of ambient temperature.
For the latest on Altech Power Supply specifications please visit www.altechcorp.com/power.
54
Mechanical Specification
133
72
118
Cat. No.: PSB-36024
TB1 Terminal Pin. No Assignment
TB1 Terminal Pin. No Assignment
Pin No.
1
2
3
Assignment
(2 phase)
N/L
L/L
FG
Pin No.
1,2,3
4,5,6
7,8
Assignment
DC output -V
DC output +V
DC OK relay contacts
DC OK Relay Contact
Outputs are used for preventive function monitoring of the
power supply. An electrically isolated signal contact is
available. The signal contact closes when the output
power is OK and opens when the output voltage falls
below 20Vdc ±5%.
Output Voltage vs. Output Current, typ.
Out Voltage
28
24
20
16
12
8
4
0
0
10
20
30
40
Load (A)
Output Derating Curve
Parallel Connection
A parallel connection with the same model
power supply can be set up to increase the
output power. The output has to be adjusted
approximately to the same value (± 20mV) while
applying a 1-2 A load to all devices before
connecting them in parallel. In PSA-600xx, for
more power, the position of the Easy Parallel
jumper needs to be changed to enable a parallel
connection. In this mode up to 4 power supplies
can be put together in parallel.
AC
DC
AC
DC
+
–
+
–
+
–
LOAD
REMOVE FOR
PARALLEL
CONNECTION
Easy Parallel conenction
OFF (factory selection)
Vadj
REMOVE FOR
PARALLEL
CONNECTION
Easy Parallel
ON
Vadj
Note: All dimensions are in millimeters, to convert to inches multiply by 0.03937.
Altech Corp.
®
• 35 Royal Road • Flemington, NJ 08822-6000 • Phone (908)806-9400 • FAX (908)806-9490
55