DC-AC INVERTER UNIT
PS-DA0245-01(S)
(12 W DUAL OUTPUTS)
DESCRIPTION :
This low profile DC to AC Inverter is developed for quad lamps.
Optimzed for Sharp LQ150X1LGN2A
APPLICABLE LCD:
Lamp Voltage 1050 Vrms
Lamp Current 2 x 4.5 mArms
Lamp Start Up Voltage 2.400 Vrms (Vin : 12 Vdc)
FEATURES :
Wide Operating temperature range
Alarm signal function
PWM dimming type.
Current Feedback Circuit
Remote ON/OFF
Open Lamp Detection
Extra high starting Voltage
RoHS compliant (S)
TEMPERATURE & HUMIDITY :
Operating Temperature Range
Storage Temperature Range
Humidity
DIMENSIONS :
LxWxH
(PRELIMINARY INFORMATION)
0°C ~ +50°C
-20°C ~ +85°C
95 %RH max
130 x 40 x 9 mm
Unit : mm
Weight :28 (g) typ.
Note: Please use plastic screw in case of a non-insulating mounting base!
Components
No.
1
2
3
Part Description
PCB
Connector CN1
Connector CN2 + CN3
Qty.
1
1
2
Material
UL94V-0 (FR-4 or CEM-3)
S7B-PH-SM3
SM02B-BHSS-1-TB
Note
t=1m m
JST or equal
JST or equal
Power Systems – The Power Solution
Web:
Email:
www.Power-Systems.de
Info@Power-Systems.de
Page (1)
Address: Hauptstr. 48 ; 74360 Ilsfeld-Auenstein / Germany
Tel. :
+ 49 / 70 62 / 67 59 - 6
Fax:
+ 49 / 70 62 / 67 59 - 800
Version 1.5.2, 28th February 2008
All specifications are subject to change without notice.
DC-AC INVERTER UNIT
PS-DA0245-01(S)
(12 W DUAL OUTPUTS)
Input side CN1:
Pin No.
CN 1-1
CN 1-2
CN 1-3
CN 1-4
CN 1-5
CN 1-6
CN 1-7
Symbols
Vin
Vin
GND
GND
Vbr
Vs t
Vrm t
Ratings
10,8 ~ 13,2 Vdc
10,8 ~ 13,2 Vdc
(PRELIMINARY INFORMATION)
Output side CN2:
Pin No.
CN 2-1
CN 2-2
Symbols
Ratings
Vhigh
1050 Vrm s (4.5 m Arm s )
GND
-
Output side CN3:
0 ~ 5.0 Vdc
0 / 5 Vdc
0 ~ 0.4 = OFF / 2.5 ~ Vin = ON
Pin No.
CN 3-1
CN 3-2
Symbols
Ratings
Vhigh
1050 Vrm s (4.5 m Arm s )
GND
-
ELECTRICAL CHARACTERISTICS :
Conditions
Parameters
Output Current
Output Current
Input Current
Input Current
Frequency
Open Circuit Voltage
No load Shutdown
Symbols
Iout
Iout
Iin1
Iin2
F
Vopen
Tsd
Vin (V)
12±1.2
12±0.6
12±1.2
12±1.2
12±1.2
11.4
12±1.2
Vbr (V)
5.0
0.0
5.0
5.0
5.0
5.0
5.0
Tu (°C)
0 ~ +50
0 ~ +50
0 ~ +50
0 ~ +50
0 ~ +50
0 ~ +50
0 ~ +50
Min.
4.0
-
-
40
2.200
-
Specification
Typ.
4.5
13
1.01
-
50
2.400
1.0
Max.
5.0
1.3
1.0
55
2.600
-
Unit
mArms
%
Adc
mAdc
kHz
Vrms
sec
Note
Dut y 100%
Duty min
wit hout load
Note 1 :
Note 2 :
Note 3:
Please keep minimum of 2mm clearance (all directions) between inverter high voltage area as
marked on mechanical drawing and any conductors.
Open circuit on all lamps for more than 3 sec., will shut the inverter down.
Before apply any control signal into inverter, please provide Vcc first. Please follow the reversed
sequence during power off. Power off control signal first, then power off Vcc.
TEST CIRCUIT :
F
Iin
V
F
CN2-1
1000:1
PROBE
SW2
Vopen
V
~
Vin
10.8 ~ 13.2 V
A
CN1-1
CN1-2
CN1-3
CN1-4
T1
SW 1
RL1
CL1
Operation of unit
Operation
Non operation
a
b
Iout
1
A
~
CN2-2
SW3
CN1-5
Vbr
0 ~ 5.0 Vdc
SW4
CN3-1
Vst
5 Vdc V
Vrmt
0 / 5 Vdc
V
CN1-6
RL1
CL1
a
b
SW1
CN1-7
CN3-2
SW5
A
~
Iout
1
Power Systems – The Power Solution
Web:
Email:
www.Power-Systems.de
Info@Power-Systems.de
Page (2)
Address: Hauptstr. 48 ; 74360 Ilsfeld-Auenstein / Germany
Tel. :
+ 49 / 70 62 / 67 59 - 6
Fax:
+ 49 / 70 62 / 67 59 - 800
Version 1.5.2, 28th February 2008
All specifications are subject to change without notice.
DC-AC INVERTER UNIT
BACKLIGHT INVERTER INSTALLATION INSTRUCTION
Precautionary Notes Regarding the Use of This Inverter
When using this product, give due consideration to the precautionary notes described below
and ensure a safe design. Inappropriate use may result in electric shock, injury or fire.
WARNING
• This product is subject to high voltage. Do not touch it while the power is on. Failing to do so may result in electric shock.
CAUTION
• This product is designed for the lighting of a Cold Cathode Fluorescent Lamp. Do not use it with any other load.
• Store this product under the conditions defined in the specification document.
• Do not store this product in an environment where dust, dirt or corrosive gas (salt, acid, base, etc.) is present.
• This product is subject to high voltage. If there is a possibility that the user may touch the product, provide a proper
indication in order to draw the user’s attention.
• This product is designed for use with general electronic equipment. If it is to be used with medical equipment that directly
affects human life or for the control of transportation equipment to which passengers entrust their lives, provide thorough fail-
safe measures.
• Avoid using this product under high temperatures or high humidity or in an environment in which dust, dirt or any corrosive
gas (salt, acid, base, etc.) is present. Also, be careful not to allow the formation of dew condensation. It may result in
damage or electric shock.
• If the product does not have a built-in protective circuit (circuit breaker, fuse, etc.), it is recommended that a fuse be used at
the input stage to prevent the generation of smoke or fire in the event of a malfunction. Even when the product has a built-in
protective circuit (circuit breaker, fuse, etc.), the circuit may not function properly due to inappropriate operating conditions or
power-supply capacity. It is recommended that an appropriate protective circuit (circuit breaker, fuse, etc.) be provided
separately from the built-in circuit.
• Use the product only within the specified input voltage, output power, output voltage and operating temperature ranges.
Exceeding these values may result in damage, etc. Abnormal voltage may result in damage, etc.
• Provide a measure for the preventation of surge voltage due to lighting, etc. Abnormal voltage may result in damage, etc.
• To prevent problems arising form short-circuiting of the high-voltage section, provide appropriate measures to prevent the
entry of foreign substances following installation.
• This product is not designed to provide resistance to radiation.
HANDLING PRECAUTIONS
• This product uses thin wires. Observe the following precautions and handle it with care so as not to cause wire breakage.
Broken wire may result in damage, etc.
Do not stack multiple products on top of one another,
Do not allow the product to come in contact with tools, etc.
• Do not apply excessive stress during installation. It may cause chipping and cracking, resulting in damage, etc
• Provide a clearance of 2 mm or more between the high-voltage section of this product and the frame body on which the
product is installed and also the conductor section (pattern, pad, etc.)
Power Systems – The Power Solution
Web:
Email:
www.Power-Systems.de
Info@Power-Systems.de
Page (1)
Address: Hauptstr. 48 ; 74360 Ilsfeld-Auenstein / Germany
Tel. :
+ 49 / 70 62 / 67 59 - 6
Fax:
+ 49 / 70 62 / 67 59 - 800
Version 2.0, 15th August 2007
All specifications are subject to change without notice.
DC-AC INVERTER UNIT
Thank you very much for usually patronizing Power Systems and TDK’s DC/AC inverter. Following the expansion of it’s use, there
are unexpected troubles that are caused by mis-use or mis-handling because the DC/AC inverter generates a high voltage of
900Vrms or more. Hereafter, the cases of the major troubles are described. Please also refer to “Notes of used” of the attached
paper.
Ex.1 Multilayered PWB
Inverter was mounted the nearest to the main board because there is no surface pattern. However, dielectric breakdown
happened because there was a low-voltage pattern in internal layer, and they were damaged by arc fire.
Ex.2 Foreign body
Short of high voltage area by insect (cockroach etc.) having invaded installed set in food processing plant and counter, etc. Short
by adhesion of metal powder when using it by set such as NC machine tool.
Ex.3 Mechanical stress
Parts will be cracked or the wire of transformer will be broke, etc. When the mechanical stress was given at the installation on the
set.
Ex.4 Storage, handling
When you store it, if the product is piled up or grabed with other inverters together at once, etc. these will be the cause of the
break of transformer’s wire and etc.
CABLES CONNECTION
1.)
Don‘t extand cables.
1.1.)
Don‘t cut through nor solder them, unless you have consulted the manufacture.
2.)
Don‘t exchange cables.
2.1.)
Polarity is very important otherwise -will be able to a short circuit.
-there might be a short circuit.(Please refer to fig.1)
Fig. 1
OK
NG
Power Systems – The Power Solution
Web:
Email:
www.Power-Systems.de
Info@Power-Systems.de
Page (2)
Address: Hauptstr. 48 ; 74360 Ilsfeld-Auenstein / Germany
Tel. :
+ 49 / 70 62 / 67 59 - 6
Fax:
+ 49 / 70 62 / 67 59 - 800
Version 2.0, 15th August 2007
All specifications are subject to change without notice.