桂花蒸
Air pressure control device
1. System framework
    This device is an air bag air pressure control device, mainly composed of STM32F103C8T6 microcontroller, BMP388 air pressure sensor, OLED display module, elastic buttons, TB6612 drive module, air pump, solenoid valve, and air bag.     Among them, one end of the air guide pipe is connected to the air pump, and the other end is connected to one end of the one-way valve to prevent air flow in the opposite direction. The air guide pipe led from the other end of the one-way valve is connected to the three air guide pipes through a multi-way joint, and one is connected to the pressure sensor, One is connected to the solenoid valve and the other is connected to the air bag.
2. Function description
    This air pressure control device detects the air pressure value in the air bag through the BMP388 air pressure sensor, and displays the detection results on the OLED screen in real time. This device can set the target air pressure value, inflate the air bag through the air pump or open the solenoid valve to deflate so that the air pressure in the air bag reaches the set value, and adjust the inflation speed by adjusting the speed of the motor in the air pump. When the sensor detects that the air pressure value deviates from the set value, the air pump is used to inflate again or the solenoid valve is opened to deflate to suppress changes in air pressure and maintain dynamic stability. The air pressure range that this device can accurately measure is 30.0~125.0kPa, and the target air pressure range that can be adjusted is the current atmospheric pressure (approximately 101.3 kPa)~125.0kPa. In addition, this device also has a Bluetooth module to facilitate connection with a smartphone, thereby enabling detection and adjustment of the air bag pressure through the mobile app ( the Bluetooth function is not implemented ).
4. Debugging and test results
  • The test comparison of different flow rates at the same target pressure (110.0Kpa) is as follows:
flow rate Start air pressure target air pressure end air pressure average time
weak 101.3Kpa 110.0Kpa 110.0±0.1Kpa 40s
middle 101.3Kpa 110.0Kpa 110.0±0.1Kpa 9s
powerful 101.3Kpa 110.0Kpa 110.0±0.1Kpa 3.5s
  • The test comparison of the same flow rate at different target air pressures is as follows:
weak 101.3Kpa 105.0Kpa 105.0±0.1Kpa 19s
weak 101.3Kpa 115.0Kpa 114.9±0.1Kpa 110s
middle 101.3Kpa 105.0Kpa 105.0±0.1Kpa 6s
middle 101.3Kpa 115.0Kpa 115.0±0.1Kpa 13s
middle 101.3Kpa 120.0Kpa 120.0±0.1Kpa 18s
powerful 101.3Kpa 105.0Kpa 105.0±0.1Kpa 2.5s
powerful 101.3Kpa 115.0Kpa 115.0±0.1Kpa 6.0s
powerful 101.3Kpa 120.0Kpa 120.0±0.1Kpa 7.3s
  • Result analysis
    After many times of debugging and testing, this device has basically achieved the functions required by the question. At the same time, it was found that under weak flow rates, it is difficult for the air pressure in the air bag to continue to rise after reaching 115Kpa; under medium and strong flow rates, it will become difficult for the air pressure inside the air bag to rise after reaching 121 Kpa.
    If further improvement is needed in maintaining stable air pressure: the air duct connection can be sealed to improve the air tightness of the device. If you have different requirements on the air pressure adjustment range: you can replace the BMP388 with an air pressure sensor with the required range, and select an air bag with appropriate pressure resistance.